Answer / carl_ellis
Configuring the range for a DP transmitter
Open tank:
- Flanged DP transmitter
- high side at lower flange
- no remote seals:
- units: water column units = uwc
- LRV = 0.00 uwc
- URV = physical upper level elevation (uwc) * specific
gravity of fluid
Closed tank:
- flanged DP transmitter
- high side at lower flange
- no remote seals
- dry leg from vapor space above liquid is piped/connected
to the low side
- LRV = 0.00 uwc
- URV = physical upper level elevation (uwc) * specific
gravity of fluid
When the receiver (DCS/PLC/indicator/recorder) receives the
level signal, it converts to physical level elevation by
dividing the process level signal by the specific gravity
and scaling to physical level units.
Volumetric flow rate with DP transmitter on DP flow element:
- units: water column units = uwc
- LRV = 0.00
- URV = maximum DP value at the maximum flow rate stated
on the sizing sheet of the DP flow element
Whether the signal is square rooted in the transmitter or
in the receiver for conversion to flow rate is up to the
plant convention/standards.
Is This Answer Correct ? | 2 Yes | 5 No |
What are the type of bonnets in the control valves?
What is the difference between relative vibration
why we are using (-24VDC) and where we r using plz tell me
wht is dcs architecture ? can u give example?
If the Barrier Fails during online then What will be the control valve position in field or Positioner action in the field.
what is compensation in engineering and what is temperature compensation?
What is mean by ATEX?
Whether the DI, DOs shields can be connected with Analog Input Shield Earthpit?
I need the intools training institute address in india. Intools subject oriented local authors books.Refer me plz
In a gas over oil actuator, after the opening/closing of valve, how the gas is vented out? How does the hydraulic/gas circuit function?
Can anybody tell me how to select the size of earthing cable for DCS & PLC system.Please tell me any relevant answer here or mail it to me.
Why the ammonia and Nitric Acid level indicators is with millimeter ? and What is the conversion form millimeters that level indicator indicate to weight ?