How the flow can be measured by using DP Transmitter?
Answers were Sorted based on User's Feedback
Answer / mobin ahmed sabayek
for flow measurment first need creat difrential pressur by
using of orific plat in flow path dp tranmitter have low
and high side cannect high pressure and cannect low side of
low presure of tapping and transmitter will convert
diffrential pressure in to 4 -20 ma
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / ashish namdev, bina refinery [
A DP type transmitter senses DP pressure from LP & HP tapping.
after sensing DP we will have to change some settings in the
transmitter, the settings are as follows -
1. set the range in output block.
2. change display parameter from linear to square root.
3. change display unit as per your requirement.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / george mathews
When we are going to measure the flow using a DP
Transmitter there must b a Flow Instrument placed there. So
if we see the basic structure of a flow instrument we can
clearly see that one side the orifice is normal and it goes
on shrinking toards the other end like a conical shape.
so we connect the higher end of the dp to the normal
orifice and the lower side to the other end of the flow
instrument. and when there is a flow there ll alwyas a
difference in the pressure as soon the water/ oil / gas
enter the flow instrument the normal end is at high
pressure but the exit end is at lower pressure due to d
manufacture of the instrument. And we can get out
measurment .
Is This Answer Correct ? | 1 Yes | 1 No |
what is fire and gas system?
2 Answers Andhra Petrochemicals Limited,
What is the difference between ROM & RAM .
How to zero trim the level transmitter by using foundation fieldbus communicator.
How to calibrate Field bus transmitter? procedure ?
what is IPS (instrument protective system)?
Can any body tell me about SAP MAINTINANCE MODULE. WHAT IS its function and application. And study material Source about it. I shall be very thankful.
For 150 mtr cable run from DCS panel to transmitter (24 VDC with 4-20 ma output), need cable size. 1.5 sqmm is suitable?
how to calculate static pressure in a pipe line,when we know the DP(differential pressure) in the line, area of the pipe? please any one tell me the relation between them..?
why we use npn sensor in vibration monitoring system
3. Differentiate between ultrasonic flowmeter and radar type flow meter.
With N nodes and B branches what will have a network ???
What happen if we install my pressure transmitter below the elevation of pipe in natural gas service?