Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...



Dear all... I have 1 0-400 duplex type RTD, I connected the
A side to the temperature indicator and B side to the PLC
panel, but when I have observed then found that The PLC side
temp has the variation. and it was distub to other RTD temp
also. so what can I do.pls help me



Dear all... I have 1 0-400 duplex type RTD, I connected the A side to the temperature indicator a..

Answer / carl_ellis

An offset in readings from separate RTD's can indicate
- a difference in calibration of the analog input devices
- a bad RTD element, one that has drifted out of spec
- a common ground issue with ground loops between the analog
input devices

An RTD is supposed to be ungrounded and the two RTD's in a
duplex element are supposed to be electrically isolated from
one another, so it is unlikely the ground loop is unlikely
unless poor wiring of the extension wire or head wiring has
created a connection to ground.

If you're complaining about a small difference of the
indicated temperatures, then get out your cal gear and cal
the inputs.

To check for a bad RTD, I'd take an ohmmeter and see if any
leg on the A side has any connection to the B side by
disconnecting the wiring from each analog input and check
the resistance. If there's a low resistance, it indicates
some connection from A to B. If the extension wires are
then disconnected and the resistance is checked on the RTD
lead wires and the resistance remains, then it's a bad RTD.
If the resistance goes high (open circuit) then the
extension wire is shorting or making a low resistance
connection somewhere.

Carl Ellis
Measure First

Is This Answer Correct ?    1 Yes 2 No

Post New Answer

More Instrumentation Interview Questions

What is loop checking ?

10 Answers   Kharafi National, Petrofac, Samsung,


what are the steps to commissioning a DCS system?

2 Answers   BGR Energy,


How to Calibrate Transducers? Can you give me a step by ste procedure?

1 Answers  


what is diff between the centrifugal and reciprocating

2 Answers  


I have a problem with a valve (air to close). When it is fully closed and try to open 1% it doesn't responce till 3% open suddenly more than 3% then back to 3%. I tried to tune positioner then removed it, the problem still exist. Any idea

3 Answers  


what is the thermocuple compensation circuit

3 Answers  


What is the difference between ff transmitter and non ff transmitter

0 Answers   Samsung,


A PLC is programmed to drive three motors A, B and C as follows : After running motor A for an hour, motor B should get ON and motor A should get OFF. And after running motor B for an hour, motor C should get ON and motor B should get OFF. And after running motor C for an hour, motor A should get ON and motor C should get OFF. (That is, a cyclic repetition with time period one hour) Now, the second condition is: If any motor gone faulty and is tripped, the consecutive motor should get ON and the faulty (tripped) motor should be eliminated from cyclic repetition. The remaining two motors should bear the cyclic repetition of one hour each. (For healthy motor take logic as high and for tripped motor take logic as low) Now, the third condition is: When motor A load(Amps) exceeds 60% of its rated load, motor B should get ON in parallel to motor A. And when both motors A & B are running in parallel, and if their load exceeds 60% of their rated load, motor C should also start in parallel to A & B. [Here the cyclic repetition is eliminated, until their loads become normal(40%)] [Take logic high(1) for load at 60% and logic low(0) for load at 40%] Now draw a flow chart or a ladder diagram to fulfill the above condition.

0 Answers   MNC,


Can Any body tell me about the Contact or Email id of any good Consultancy which help me to find a job in Instrumentation Field in India .I have Six years of Work Experience in the Same field.Please revert me back on shammi_gwalior@yahoo.com ?

0 Answers  


how to calculate range of level transmitter?

0 Answers   TCE,


what is the formula for changing Range of Transmitter from X mmwc to some Y mmwc with respect to DCS NCMH flow range from x NCMH to y NCMH?

1 Answers   HCL,


what is coriolis principle for mass flowmeter?

5 Answers   ABB,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)