I have a problem with a valve (air to close).
When it is fully closed and try to open 1% it doesn't responce till 3% open suddenly more than 3% then back to 3%.
I tried to tune positioner then removed it, the problem still exist.
Any idea
Answers were Sorted based on User's Feedback
There can be may issues :
1) Very first indication is that your plug and seat are having some foreign particles or uneven surface which is restricting the valve for initial opening.
2) Check the springs of the actuator for any crack as when pressure is increased it lifts the valve.
3) Check for positioner relay.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / smith
which type of positioner you are using?. it depends on the positioner. try to tune it correct manner you will get the output.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / praveen kumar
first decoupled the actuator then ensure and mark on the stem of full opening and closing, then couple the actuator stem and plug on fully 100 % open of marking position. finally to ensure zero passing test.just close the control valve and fil the water on bonnet inlet.same passing tht u feel means place the nut or iron piece something inb/w the coupling.then ensure again on zero passing test.if again feel the passing means pls to do lapping on seating...then take an trail.
| Is This Answer Correct ? | 0 Yes | 0 No |
How vortex sensor used for steam flow measurment can be checked on line i.e without taking out from process line.
What is difference of fanuc alpha series 16i and 18i controller.also what is differnce betn TC and MC controller
where i can get training in INTOOLS and PDMS in Delhi-NCR OR north part of India. please reply with ur ans. at arunsamkaria@ymail.com
Why is a dead weight tester so called by that name?
where uses EXe /EXd/Exo/Exn/Exp/Exq/EXia
in any transimitter (flow/level) there are three terminals for supply& test (+,-,+)in two wire,24VDC given to Tx.,but how 4-20 ma signal travels thru same wire (as it is for 24VDC input supply)?
why fuse block is not used for AI signal?
radial & axial vibration sensor output voltage is ac or dc volt?
What is rtd output signal
i have 20 kw motor & my vfd drive capcity is 18 kw if possible to use 20kw motor on this vfd?
What is the meaning of Dry contact and Wet Contact related to to sensors?
How to Calibrate Vibration Probe (Axial, Redial) in field
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)