why do we use 4-20mA as o/p and why don't use 0-20mA or 5-
21mA?
Answers were Sorted based on User's Feedback
Answer / ahmed eid
Ohm's law voltage = current * resistance
of the standerd voltage in the dcs from 1 to 5 voltge
and the standerd resistance of loop 250 oums
so
V=I*R
the first in the low signal 1 volt
1(v)=I*250(r) =.004 A
.004*1000 = 4 MA
the sacand in the high signal 5 volt
5(v)=I*250(r) = 020 A
.020*250 = 20 MA
| Is This Answer Correct ? | 19 Yes | 0 No |
Answer / d tilston
Two wire transmitters require some power to work. 0-20 mA
would not provide any power at 0 mA.
Power = current x volts, (usually 24 VDC)
Power = 0.004A x 24VDC
Power = 0.096W
Not much power.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / carl_ellis
Question:
why do we use 4-20mA as o/p and why don't use 0-20mA or 5- 21mA?
There are systems that use 0-20mA as an output from a
controller. Those are active', powered outputs, not
signals from 2 wire, loop powered field transmitters. 2
wire, loop powered instruments use about 3.5mA to power the
transmitter's electronics, so 2 wire, loop powered
instruments can never go below 3.5mA without losing the
current needed to power the instrument.
An active analog output from a controller that uses the
controller's power from the controller to drive the current
signal can be a 4-20mA signal or a 0-20mA signal.
People in the process industries use the 4-20mA output
because it is a 'live-zero' that immediately indicates a
broken wire or an open circuit if the loop current falls to
0.0mA. Those using 0-20mA probably have a 0-10Vdc or 0-5Vdc
analog input and want to use the entire span with a 500 ohm
or 250 ohm resistor.
As to why 5-21mA is not used, there are conventions used
that make systems maintainable over time. If every analog
output used oddball ranges or spans, it would be near
impossible to maintain the system over time. Given that
many control systems operate in excess of 10 years, it is
important to use standard analog signals in order to keep
the system maintainable.
The convention is 4-20mA, established by the ISA SP-50
standard in 1967. Deviations are punishable. Be warned.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
What is the difference bitween control net scaner and device net scaner
what is dry leg and wet leg in transmeter calibration?
how to measure oxygen which methods are using?
How to decrease opening & closing time of on/off valve?
1)unmovable objects have frequency or not?if that object have frequency,how do we measure and transmit? 2)how do u measure the continuity without multimeter? 3)we put 24volt dc supply in railway track how many distance it is traveled without voltage drop?
how we calculate the range of flow from a dp?i mean if we have a dp,3810mm h2o.how much flow ranges we can use for this DP?
How to get Cv of control valve having following parameter ,i.e inlet pressure 4.5kg/cm2 outlet pressure 1 kg/cm2 specific gravity 0.808
what is the meaning of wet leg & where is it used?
Q- What are the application in which PNP transistor is preferred over NPN ?
can we change the range of 3151 model level transmitter of rosemount make? present calibration range is 1000mmwc and want to change it to 2000mmwc
square root calculation for dp flow transmitter? give me a explanation with example
what different types of problems do occur while doing instrumentation commisioning and how to solve them? please explain in detail
0 Answers Process Control Technologies,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)