why do we use 4-20mA as o/p and why don't use 0-20mA or 5-
21mA?

Answers were Sorted based on User's Feedback



why do we use 4-20mA as o/p and why don't use 0-20mA or 5- 21mA?..

Answer / ahmed eid

Ohm's law voltage = current * resistance
of the standerd voltage in the dcs from 1 to 5 voltge
and the standerd resistance of loop 250 oums
so
V=I*R
the first in the low signal 1 volt
1(v)=I*250(r) =.004 A
.004*1000 = 4 MA
the sacand in the high signal 5 volt
5(v)=I*250(r) = 020 A
.020*250 = 20 MA


Is This Answer Correct ?    19 Yes 0 No

why do we use 4-20mA as o/p and why don't use 0-20mA or 5- 21mA?..

Answer / d tilston

Two wire transmitters require some power to work. 0-20 mA
would not provide any power at 0 mA.

Power = current x volts, (usually 24 VDC)
Power = 0.004A x 24VDC
Power = 0.096W

Not much power.

Is This Answer Correct ?    4 Yes 0 No

why do we use 4-20mA as o/p and why don't use 0-20mA or 5- 21mA?..

Answer / carl_ellis

Question:
why do we use 4-20mA as o/p and why don't use 0-20mA or 5- 21mA?

There are systems that use 0-20mA as an output from a
controller. Those are active', powered outputs, not
signals from 2 wire, loop powered field transmitters. 2
wire, loop powered instruments use about 3.5mA to power the
transmitter's electronics, so 2 wire, loop powered
instruments can never go below 3.5mA without losing the
current needed to power the instrument.

An active analog output from a controller that uses the
controller's power from the controller to drive the current
signal can be a 4-20mA signal or a 0-20mA signal.

People in the process industries use the 4-20mA output
because it is a 'live-zero' that immediately indicates a
broken wire or an open circuit if the loop current falls to
0.0mA. Those using 0-20mA probably have a 0-10Vdc or 0-5Vdc
analog input and want to use the entire span with a 500 ohm
or 250 ohm resistor.

As to why 5-21mA is not used, there are conventions used
that make systems maintainable over time. If every analog
output used oddball ranges or spans, it would be near
impossible to maintain the system over time. Given that
many control systems operate in excess of 10 years, it is
important to use standard analog signals in order to keep
the system maintainable.

The convention is 4-20mA, established by the ISA SP-50
standard in 1967. Deviations are punishable. Be warned.

Carl Ellis
Measure First

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

what is sequence table in DCS . make a logic in sequence table for tripping of ID fan in Boiler(in YOKOGAWA CS 3000 DCS).

1 Answers   Yokogawa,


what is difference between HART communication and BRAIN communication?

1 Answers   Delta Controls,


how to calculate interface capelary level transmetar lower S.G.0.54 and uper S.G. 0.26 and h=490 mm

3 Answers  


HOW TO CALCULATE ACCURACY OF AN INSTRUMENT. WHICH IS COMPITABLE FOR USE.

0 Answers   ABB, NTPC,


How many interlocks at turbine side?

0 Answers   Edac, SRF,






What are primary elements of measuring pressure?

0 Answers  


what is the difference between mmhg & mmwc?. i want to calibrate a transmitter in the range of -100 to 300 mmwc. Which is the reference for calibrate the Tx,if mmwc not available?. Is it mmhg or mmho2?.

3 Answers   UPL,


In s7-200 we use HMI TD-200C , what that C stands for........ plz reply

2 Answers  


how u calibrate sox nox co2 co in cemps?what is opacity n HPm?tell the standard parameters of cems?

0 Answers  


how to work gas chromatography explain principle ?

2 Answers  


What are the logic behind 2x2 and 2x3 logic and more when ask in interviews

1 Answers   Reliance,


How we select the range of level transmitter in closed vessel ?

4 Answers   Rosemount,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)