Answer / ginoop .k.m
ma (Linear) =(% *
16)/100 +4
example - ma=
(25*16)/100 +4
linear ma of 25%
=400/100 +4
linear ma of 25%=
4+4
linear ma of 25% =
8ma
ma (sq rt) = (sqrt
of %*16)/10 +4
example -
sqrt ma of 25% =
(sqrt
of25*16)/10 + 4
sqrt ma of 25% =
(5*16)/10 +4
sqrt ma of 25% =
8+4
sqrt ma of 25%
=12ma
Is This Answer Correct ? | 45 Yes | 7 No |
Answer / sampath
Sq.Root { x / 100 } * 16 + 4 = ____ mA
where, x is the % ( percenteage value )
For eg, 25% Sq.Root { 25 / 100 } * 16 + 4 = 12 mA
50% Sq.Root { 50 / 100 } * 16 + 4 = 15.31 mA
75% Sq.Root { 75 / 100 } * 16 + 4 = 17.86 mA
Is This Answer Correct ? | 51 Yes | 23 No |
Answer / jackass
So, the way you would go about doing square root extraction is by using an analog multipler. An analog multiplier has three inputs Vx, Vy & Vz. The output is given by Vo = (Vx*Vy)/Vz; If we set Vy = 1V and Vo = Vz through a feedback loop, we get Vo.^2 = Vx => Vo = sqrt(Vx).
If the interviewer further asks about an analog multiplier, you could mention that it can be designed by a combination of logarithmic/anti-logarithmic amplifier and an adder.
Hope that helps!
Is This Answer Correct ? | 2 Yes | 14 No |
A pressure differential gauge type of instrument has a manifold with 2 isolation valves (hp and lp),2 vents(1 each for hp and lp) and 1 equalizing valve. Determine the position of each valve(either fully closed or fully open) when troboulshooting to: 1. zero the transmitter. 2. determine if there is a block in the impulse line. 3. determine if the gauge is functioning properly. The process fluid is water.
GWR radar transmitter working principle?
What is Vena contracta?
Is it possible to drill additional gland hole in EExd or EExe JBs? What are the points to take care?
how to calibrate steam control valve in steam turbine
what is the advantage by using PID controller than P& PID?
plz exlain the dcs system of ABB sympony hamnony
I have installed a RTD whose length is 2250mm(RTD stem length), but it's upper 200 -250mm is out of the reactor, and this upper 200mm stem is surrounded by atmospheric temp. And the lower portion i.e. 2000mm is in contact with the measuring fluid, then does the final measuring temp. Gonna change as the upper 200mm RTD stem is out of reactor?
1 Answers Process Control Technologies,
What is safety barrier and how it is work
What is NAMUR standard and why its allways reletad with Sollenoid
I have flow transmiter DP range is 0 to 5000mmwc,(convert) Display to be show in m3/Hr.
Difference between ultra sonic flow meter