Generally LT Cable size are not calculated based on Fault current basis, Due to High Fault current on LT System. For e.g. consider that 2500 kVA Transformer, %Z = 6.25%, 415 Volts at Secondary. Fault Current at Secondary system will be 55.64 kA. Now if we would have to select the Cable size based on Fault current then it would be ---
If √t
A = ----------------- Sq.mm --- For XLPE Cable Aluminum Conductor
0.094
585 sqmm, nearest standard rating of cable is 630 sqmm. Hence Commercially as well as laying point of view the same is not recommended nor as per good engineering practice.
HT Cable Sizing :
Cable sizing based on Fault current is possible In HT System, based practically and commercially point of view. Consider that 11kV system is feeding the power supply. As per IS 2026, 11kV Power system will have max 500MVA Fault Level. It means it will have 26 kA. 300sqmm cable will be sufficient to withstand 26 kA for 1 Sec.
Summary : System Design shall not be strictly as norms, it should be design considering Laying / installation, Practically and Commercially viable.
Regards
Sudhanva Madhukar Mahamuni
electricmahamuni@gmail.com
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / xyz
Short Circuit withstand capacity is to be checked for HT
cables. For LT breaker controlled motor feeders, the cable
impedance reduces short circuit current considerable, hence,
short circuit withstand capacity is not required to be
checked for the rated fault level of the LT motors.
| Is This Answer Correct ? | 3 Yes | 5 No |
how can we choose the size of road crossing pipe for power cables
I WANT YHE TECHNICAL AND ELECTRICAL SPECIFICATIONS OF 2x4MW 11KV 2x10MW 11KV 2x25MW 11KV 2x100MW 11KV HYDEL POWER PLANT i.e PROTECTION SYSTEM,MONITORING,CONTROL SYSTEM,GENERATION,SYNCHRONISATION,METERING PLEASE SEND THE DETAILS TO MY MAIL ID SPRAVEEN_222@YAHOO.CO.IN
How will you Protect aeroplanes and Ships from Lightining?
why is electricity produced and distributed in multiples of 11. 440V, 11KV, 22KV, 132KV etc
what is transformer
What will happen if mains neutral and generator neutral shorted?
what is the difference between skin effect
Ho de we calculate the line loss of a 500 kv line over 1000km.
plz send me the syllabus or any sample paper for engineer trainee recruitment if any,on ravinder911@yahoo.com
0 Answers Bhel, Maruti Suzuki,
Mention the disadvantages of low power factor?
what is mean by xlpe swa pvc
1.what is the contact resistace of CB ? 2.radioactivity should be mesured with---------?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)