in control valve is constructed as per API 6D or API 6A,
then which standard is used for fire testing of valve?.
Answer / mahesh
If Control valve is constructed as per API 6D pr API 6A then fire testing of valve shall be as per the ISO 10497 or API 607
Is This Answer Correct ? | 1 Yes | 0 No |