Why we use 4 - 20 ma?
Answers were Sorted based on User's Feedback
Answer / sam daniel, marthandam, kanyak
To operate a Digital signal we need 1-5Vdc. For Analog
Instruments we are using 250 ohms as load resistance. When
we converting this signal into current By Ohm's
Law V=IR
I=V/R
Put, V=1V Then I=1/250=4mA
Put, V=2V Then I=2/250=8mA
Put, V=3V Then I=3/250=12mA
Put, V=4V Then I=4/250=16mA
Put, V=5V Then I=5/250=20mA
*Also, since this is linear region
*Not possible to cause spark
*Since it is a current signal we can transmit it into long
distance.
*Suppose if the instrument is dead we can identify it.
| Is This Answer Correct ? | 62 Yes | 3 No |
Answer / jayaraj
1}///in earlier days we had used BJT transister in signal
conditioning circuits for amplification purposes so in BJT
transfer characteristics 4 to 20 milli amps is a linear
region,....but now-a-days we re using cmos only.... as a
convention only we are following this 4-20 range
2}///another reason...for not using 0 milli amp
coz if we use like that we cannot distinguish between true
signal zero and dead zero(break in wires)
| Is This Answer Correct ? | 46 Yes | 2 No |
Answer / nileshkumar
1) 4 - 2 ma signal can transmited long distance without
signal drop in cable.
2) To operate a Digital signal we need 1-5Vdc. For Analog
Instruments we are using 250 ohms as load resistance. When
we converting this signal into current By Ohm's
Law V=IR
I=V/R
Put, V=1V Then I=1/250=4mA
Put, V=2V Then I=2/250=8mA
Put, V=3V Then I=3/250=12mA
Put, V=4V Then I=4/250=16mA
Put, V=5V Then I=5/250=20mA
*when two connection short no sparking.
*Since it is a current signal we can transmit it into long
distance.
*Suppose if the instrument is dead we can identify it.
| Is This Answer Correct ? | 5 Yes | 1 No |
in 4-20ma we can easily check the zero and wire breaking in
transmitter. Analog card accept 1-5v dc supply. thatsy V-IR
I=V/R
V=1V R=250OHMS
1/250 = 4MA
V=2V THEN I=2/250 = 8MA
V=3V THEN I=3/250 =12MA
V=4V THEN I= 4/250 =16MA
V=5V THEN I=5/250 = 20MA.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / anish kumaran r
Live zero and minimum current required to keep alive the tx
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / suresh nagdeo
another reason from starting current from 4 ma is between two cables maximum induced current is always below 4 ma. if electrical and instrumentation cables running together this type problems arised.
| Is This Answer Correct ? | 0 Yes | 0 No |
why we use 0.2 to 1.0 kg/cm2 output in control valve
what is meant by calibration
What is the maximum distance limit of 4-20mA and 0-10V DC standard signal transmission ?
what the pid setting in controller
What is the relation between electronics & instrumentation
how eddy current loss in probe and induced gap voltage accros probe trip and shaft
whether radar level transmitter is applicable for the open tank
Is there any temperature compenasation for the air flow from FD fan & SA fans which supplies air to the Boiler?
how its work inductive proximity sensor explain briefly?
What is impulse line size
how to calibrate temprature switch and flow switch ?
what r the different types of instrumentation cables? give their specification?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)