why we use 0.2 to 1.0 kg/cm2 output in control valve
Answers were Sorted based on User's Feedback
Answer / pankaj nandasana
As you know....0.2 to 1 kg/cm2 is equal to 3-15 psig..
Generally we are considering this range...reasons are following...
1) Suppose if your have set lower limit at 0 psig, then how you can differentiate zero signal level and pipe breakage..!!!! You can not distinguish two thing..That why we select some elevated range from 0 psig.
2) Our all instrument are producing linear response in the range of 3-15 psig.
3) Pneumatic supply to all instrument is 20 psig..so alway there is bleading of air from instrument..for standardlisation purpose all are considering 3-15 psig..
Is This Answer Correct ? | 33 Yes | 0 No |
Answer / ashish namdev, bina refinery [
The diaphragm design of all control valves are universal and
the out of the actuators are 3 to 15 psi.When more than the
15 psi pressure is acting to the diaphragm that will lead it
to faulty so we use the 0.2 to 1.0kg/cm2 for control valves.
Is This Answer Correct ? | 1 Yes | 2 No |
Answer / s k
because the control valve work within the specified pressure
range of about 0.2 to 1.0 kg/cm2.
Is This Answer Correct ? | 2 Yes | 8 No |
What is force balance principle?
What is electronics?
how to calibrate differential pressure switch
If you SOURCE your outputs from a PLC, would you have to make the output HIGH, or LOW, in order to switch an output ON?
what is the difference b/w wet leg & dry leg level method
in natural gas indirect water bath heater,how to prevent the problem of backfire from firetube during ignition...becoz of this backfire performance of wbh is going low.
I am manjunath having exp in maintenance of chemical plants,know i want to do a design course INTOOLS,after doing design course can we get jobs in design field.sinve i dont have design exp..
how to rectify the poor signal strength in utrasonic digtial flow meter ,model:ge digital xce868i
Working principle of magnetic flow meter ......and calibration procedure of e+h magnetic flowmeter...
What is the input impedence of an OPAMP as an ideal device.
What are the instrumental diagram of valve.
Actual using of tube bender to bend 2 opposite 90 deg at correct measurement center to center of tubing.