Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why CT ratio stand for 50/5, 100/5, 25/5.

Answers were Sorted based on User's Feedback



why CT ratio stand for 50/5, 100/5, 25/5...

Answer / virendra joshi

Generally allThe CT operated meter is designed for a
capacity arround 5 A , the ct ratio 50/5, 100 / 5 means the
secondary current of the secondary winding will not exceed
more than 5A

Is This Answer Correct ?    106 Yes 17 No

why CT ratio stand for 50/5, 100/5, 25/5...

Answer / wasif

50/5 means that if 50 amps currnt will flow in primary then
5 amps current will flow in secondary. Actually it is the
transformation ratio of the ct Ip/Is

Is This Answer Correct ?    57 Yes 13 No

why CT ratio stand for 50/5, 100/5, 25/5...

Answer / jagadish

CTs are Instrument Transformers used for Metering or
sensing where the whole primary current cannot be fed into
meter or relay.Hence the same is porportionately reduced by
ratio and connected to load eg.Ammeter,kwH meter &Relay etc

Is This Answer Correct ?    27 Yes 3 No

why CT ratio stand for 50/5, 100/5, 25/5...

Answer / bibhu prasad sahu

CT is a instrument transformer which is converting high
current to low current(5amps).In power system we are using
it for metering & for function of protective instruments &
indicating lamps in control panel.These instruments
mechanism can not sustain more current than 5 amp.

Is This Answer Correct ?    21 Yes 1 No

why CT ratio stand for 50/5, 100/5, 25/5...

Answer / sanjay kumar

it is very easy to standered of primary current e.i
25,50,100,150,200,250,300,400,600,800,1000,1250,1600 and
2000 etc convert in to secondry current in perfect number
between minimum and maximum primary current, losses (i2r)
in ckt very low.
For that purpose 5 is perfect number

Is This Answer Correct ?    13 Yes 8 No

why CT ratio stand for 50/5, 100/5, 25/5...

Answer / madhu

Generally allThe CT operated meter is designed for a
capacity arround 5 A , the ct ratio 50/5, 100 / 5 means the
secondary current of the secondary winding will not exceed
more than 5A.Our kwh meter capacity max 5A so consumers more
requirement ex- 50A consumer load so our kwh meter not
measured the reading that cases using ct .ex 50/5 50a flows
in a line meter shows 5A its ratio 50/5 = 10 so ct ratio 10
ex our units 12/day multiply by 10 = 120 units/day

Is This Answer Correct ?    10 Yes 5 No

why CT ratio stand for 50/5, 100/5, 25/5...

Answer / rohitash saini

c.t is a current transfarmer which measure electrical current in system. we identify it just that 100/5than the ratio 20:1
that is when primary taken 20 amps current then secondary turn taken 5amp.when we put c.t ratio in digital meter after he showing direct reading .

Is This Answer Correct ?    9 Yes 5 No

why CT ratio stand for 50/5, 100/5, 25/5...

Answer / neeraj duklan

Generally allThe CT operated meter is designed for a
capacity arround 5 A , the ct ratio 50/5, 100 / 5 means the
secondary current of the secondary winding will not exceed
more than 5A

Is This Answer Correct ?    5 Yes 1 No

why CT ratio stand for 50/5, 100/5, 25/5...

Answer / yash

CT- Current transformer basically design for metering and sensing purpose .and KWH meter basically design for capacity around 5 A . So CT always available in ratio 5 A.

Is This Answer Correct ?    0 Yes 1 No

why CT ratio stand for 50/5, 100/5, 25/5...

Answer / mukhesh

All the cts are oparated in the ranges of primary 25 50
66 ....,depends on reqirement it is only for chekink of the
curent relesed from the t/f and it gives ratio of exactly 5
a ratio ther is no change if any increese or decreese relay
oparation will come into the picture if at any of time will
touch 5A rating high curent will devolope at time of touch
immedeaatly burnt out

Is This Answer Correct ?    7 Yes 12 No

Post New Answer

More Electrical Engineering Interview Questions

How can i run three phase bore well motor in 2 phase while i running it by using capacitor its ams increase to 23 ams the distance from motor to stater is 1600 feet

0 Answers   Private,


what maximum load will take a aluminum cable of 50mm 4 core.

3 Answers  


what is the power factor of an inductive load ? (i) Zero (ii) Lagging (iii) Leading (iv) Unity

5 Answers  


if harmonics is generates on the secondary side of transformer then why we put LC ckt on prim side?(i m talking abt rectiformer transformer)

0 Answers  


How to check the specific gravity of the two 12 V batteries connected in series to a 24 V UPS and inverter ? will we have to disconnect all the connections and turn off the UPS and inverter or not ? will we have to check specific gravities in each cell of the two batteries ? what is the name of the instrument that is used to check the specific gravity and whats the procedure to check the specific gravity with it ? thanks

2 Answers  


why capacitor bank is not used in generator power

7 Answers   Caterpillar,


out of all machines which have highest efficiency and why?

2 Answers  


How the unidirectional torque produced in dc motor

2 Answers   CGL, Sail,


WHAT IS MEAN BY MAGNETIC LOCKING

3 Answers   Bhel,


What is the difference between circuit breaker and isolator

0 Answers  


what is the purpose of taking HV test in LT panel.

1 Answers   PCE,


what is the difference between Resin Cast CT and Oil cooled CT?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)