why capacitor bank is not used in generator power
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
When the generators(gen) are connected to grid or net work
,if all the gens are run at unity pf ,there will be drop in
voltage due to inductive load in the system as the current
increases.Then to maintain system stability, LDC requests
large generating stations to increase the voltage . This
will increase the KVAR and results in lower lagging pf in
the gens. That is why the gens are designed for 0.8/0.85
pf.The pf of gens can be kept at any value by varying
excitation or resetting in APF mode.As pf control is
required by generating stations,capacitor banks are not used
.Capacitor banks can be used in the system to reduce the
inductive load but not in the gen stations.
Is This Answer Correct ? | 18 Yes | 1 No |
Answer / k.prakashchandra
Pf of generator can be brought to required value by varying
excitation.
Is This Answer Correct ? | 12 Yes | 3 No |
Answer / k.prakashchandra
If the gen is connected to grid ,its pf can be regulated by
varying the excitation or by APF mode.
Is This Answer Correct ? | 9 Yes | 1 No |
Answer / umkesh
One more question can be use Capacitor Bank in Aux consumption panels in Thermal Power plant like CHP
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
In the line 9, read as ' As pf control is not required'.
Is This Answer Correct ? | 1 Yes | 4 No |
what we happen if 400 kvar cpacitor banks are on in manual mode and there is no load on mains ??????????????
why the three phase transformer's star point does not sparks or seperated? while we often see that two phases touches each other it sparks and ocationaly conductor breakes out.
what is the voltage present in the telephone?
How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)
9 Answers Career Excellent Sdn Bhd, Neona, Northern Max Engineering, Sps Renewables, Terasaki, UEM,
What the full form of KVARs
If a current -8+6sin6t is flowing three ammeter, one is a centre zero PMMC meter, one is true rms meter and one is moving iron meter. What are the reading of these three meter respectively?
0 Answers National Insurance Company Limited,
what is the transmission loss for electrical supply? specifically a large shopping complex where the grid is half KM away, what will the % of transmission loss? is there any transmission loss for captive unit generation for above set? thanks
What will hapen if we connect more capacitors than required for powerfactor control? Exactly what will be the effect on power system?
how we can calculate cable size of 230v,1 hp single phase motor ? panel to motor distance is 25 meter
HOW TO CALCULATE THE ILLUMINATION IN INDOOR LIGHTING?
could any one explain me what power factor and where it is use ful
What are the advantages of using distance protection schemes as opposed to normal overcurrent/ earth fault protection on high voltage feeders.