why we test the core balance of the transformer?
Answer / k.prakashchandra
Magnetic balance test carried out on tr for detection 0f
shorted turns and extensive core problems such as shorted
laminations or core bolt insulation breakdown.
Is This Answer Correct ? | 1 Yes | 0 No |