how to check the insulation for motor using megger?
Answers were Sorted based on User's Feedback
Answer / omwikha
It is used to check the insulation resistance between the windings or between the windings and the earth terminal for the case of the motor. One lead of the megger is put on the earth terminal and the other lead is moved from one winding terminal to another as the megger handle is rotated for generation of voltage used for testing, the readings are noted and compared with the reference values to ascertain the condition of the motor.low values means insulation failure.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
Megger between winding terminal and the body .The voltage of
the megger should much higher than the rated voltage of the
motor.For 230and 400 V motors 500V megger is to be used.
Is This Answer Correct ? | 1 Yes | 3 No |
how to calculate of which rating transformer should be selected? take any example
which one cable has a more resistance.A big or small
transformers? power factor? machiences?
WHY MOSTLY Rph IS USED FOR CONTROL CIRCUITS AUX. SUPPLY ?
Difference Between Differential Relay and Restricted Earth Fault Relay of Power Transformers
What is the difference between Neutral and Earth
in control panel, how can i measuring the distance between one bus bar to another bus bar. then now only for bus bar. in mpcb and contactor also. that means one mpcb to another mpcb how much distance? how can i calculate that.
How many types of oil using in H/T & L/T Oil Circuit Breakers. need Explenation ?
Why ACB is used in LT why not in HT and why VCB is used in HT why not in LT
What you have to see in transformer after week, month?
why we use 50 hz frequency in india .. why not 60 hz
For single phase(phase to neutral) having potential difference 230.in three phase(phase to phase)we have 440V HOW...?