I HAVE A 1 MVA TRANSFORMER, I WANT TO KNOW THE FAULT LEVEL OF
THE SYSTEM ( WHAT IS FAULT LEVEL PLEASE EXPLAIN WITH EXAMPLE)
Answers were Sorted based on User's Feedback
FAULT LEVEL MEANS SHORT CIRCUIT CAPACITY OF TRANSFORMER.YOU
HAVE NOT MENTIONED THE VALUE OF TRANSFORMER RATIO & % OF
IMPEDENCE.ASSUMED VOLTAGE RATIO= 11KV/415 V & % OF
IMPEDENCE=6%.
RATED FULL LOAD AMP OUTPUT =1MVA/(415 X 1.732)=1391.25A
SO SHORT CIRCUIT CAPACITY OF TRANSFORMER= 1391.25/6%
=23187.44 A
IF ANY FAULT OCCURED THEN THE ABOVE TRANSFORMER WITHSTAND
THE SHORT CIRCUIT CURRENT OF 23187 A.
Is This Answer Correct ? | 33 Yes | 4 No |
1 MVA, 11/0.415kV Transformer
Full load current= 1000000/(1.732x415) = 1391.24A
% Z(Impedance)=5 (As per IS 2026 for transformer ratings of
0.631 MVA to 1.24 MVA)
Fault current= IFL/%Z =1391.24/0.05 =27.824 kA
Is This Answer Correct ? | 18 Yes | 3 No |
Answer / raj l. lahare
For correct Fault level the DATA given is not sufficient. You need to give the Voltage Ratio and the % impedance of the Transformer.
Is This Answer Correct ? | 1 Yes | 0 No |
If OLTC is in manual position there is chance to variation of voltage(Low or High)?
What is the full name of one of choke less lamp BLL
in our sub station why we step down firstly 33kv\11kv then 11kv to 430v. can we direct step down 33v to 430.v.
what is the difference between multimeter and megger?
a 440v 60hz 03 phase 100kw generator can deliver how much power in kw for 220v 60hz 01 phase load?
Can u start a tube light without a starter?
what difference between tapping -15% to +5 % and -5% to +15% tap. & how can define HV turns on maximun & minimum tap of power transformer.
define regulation
What is GNR ? How much value of ground neutral resistance?
what is the power factor
13 Answers Heidelberge Cement,
Why it is necessary to isolate fire fighting when you are taking shutdown for lv board.
why square root 2 is multiplied with line voltage in selection of LA ie 11/sqrtroot3=6.35 kv and it is multiplied with sqrt2 ie 6.35 KV*sqrt2=8.9 kv we will select 9kv.my question is why we are multiplying with sqrt 2?