Answer / n. ramesh
Power distribution network is supposed to have a voltage
drop of around 4%. As the utility provider has to assure a
three phase voltage of 415 V at consumer's metering point,
the secondary phase to phase voltage of the distribution
transformer is specifed at 4% higher than standard three
phase-phase to voltage of 415 V, which works out to 433 V.
| Is This Answer Correct ? | 46 Yes | 6 No |
Appliances rated voltage is 415V. If Trasformer is specied
at 415V, it will further drop down at receving end and
appliances may not work
To compensate Voltage drop at receiving end
| Is This Answer Correct ? | 42 Yes | 12 No |
Answer / ash
433V is the no load voltage. that is when the transformer
is supplied at its HT side but without any load connected
to the LV side.
| Is This Answer Correct ? | 18 Yes | 6 No |
Answer / sagar surve
Appliances rated voltage is 415V. If Trasformer is specied
at 415V, it will further drop down at receving end and
appliances may not work
| Is This Answer Correct ? | 15 Yes | 9 No |
Answer / gopalen sv
When the transformer is installed near to the LV distribution and no significant voltage drop occurs because of short length of cables then the problem of high voltage like 250 volts in single phase results in many fused bulbs. Motors rated at 400 V will experience 430 plus volts. Before deciding secondary voltage such conditions should be taken into account.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / andy d
It is to do with the transformer % impedance, As mentioned open circuit LV side of a transformer would measure 433V, Fully loaded the transformer volt drop is equal to the % impedance. A typical 1MVA DY11 transformer would be around 5% impedance at full load, i.e. the secondary voltage reduces voltage to 411V. This is a lower value then 415V however it is not advisable to run transformers at 100% if you want a long life.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / percy
433 IS LILNE TO LINE VALUE OF 250
415 IS NOT DIVISIBLE BY 1.732
| Is This Answer Correct ? | 3 Yes | 52 No |
How will I know that how many batteries I should connect to my UPS unit?
what is the difference between H.T Or HV lines...?
Derive the inductance of a coil in terms of its physical factors.
What is the difference between multimeter
Define delay time.
which is the best institute for PLC,SCADA,DCS in hyderabad
We have laid the single core Armoured cable 7 nos ( 2 each phase & 1 neutral ) to cater our electrical load . the issue is though we have Glanded the cable both the end also givan the earthing to the panel both the end we are facing a heavy sparking at the gland side. what could be the reason.
WHAT IS THE DIFFERENCE BETWEEN VOLTage and potential diff
what is the function AND aplication of CBCT?
Mention how NPN and PNP transistor works?
How can you sized or estimate the ligthning arrester current rating?
which type of oil is used as a transformer oil?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)