Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Why TAP changer provided in primary side of HT
transformer ? and why not in secondary?

Answers were Sorted based on User's Feedback



Why TAP changer provided in primary side of HT transformer ? and why not in secondary?..

Answer / yash

1. at HT side current value is less as compared to LT side.
2. insulatin requirement is less
3. tap changing can be smoother and it would have fine
control as no. of taps are more(due to low current)

Is This Answer Correct ?    76 Yes 3 No

Why TAP changer provided in primary side of HT transformer ? and why not in secondary?..

Answer / k. tivaganon

In theory, tap changer can be in any side of the
Transformer. Normally, for a step-down Tr., we put the tap
changer on the High Tension side due to many number of
turns of winding, in which we can tap easily. On the
contrary, if we put the tap changer on the Low Tension
side, there is not much turn of winding to use!!! For the
Distribution Tr., normally the tap changer will be NVTC- No
voltage tap changer. That is, no voltage no current go
through the tap during the change of tap position (There
will be no spark!!!!) For larger Power Tr., OLTC- On-Load
tap changer will be used. Tap will change position under
energized power.

Is This Answer Correct ?    44 Yes 3 No

Why TAP changer provided in primary side of HT transformer ? and why not in secondary?..

Answer / sanjay yadav

due to low current in HT side , Secondary side flow High
Current

Is This Answer Correct ?    51 Yes 17 No

Why TAP changer provided in primary side of HT transformer ? and why not in secondary?..

Answer / a.sundar

Because of High Voltage in primary side, it will draw less
current. While changing the tap, Due to less current
sparking occurs less.
In secoondary side low voltage, so high current in
secondary, and more sparks due to high current.

Sundaramahalingam_a@yahoo.in

Is This Answer Correct ?    31 Yes 3 No

Why TAP changer provided in primary side of HT transformer ? and why not in secondary?..

Answer / k1

There are two reasons; one reason from electrical and the
second one from practical point of view:
1- Low current on HV side makes tap changing smoother and
lowers stresses on the diverter switch.
2- HV windings are generally on the LV windings(consider
concentric HV and LV windings). Therefore the wiring of the
taps would be easier in comparison to the case where the
taps on LV side may be wired through HV windings.

Is This Answer Correct ?    7 Yes 6 No

Why TAP changer provided in primary side of HT transformer ? and why not in secondary?..

Answer / naaz

Because of in HT side voltage is large and current are less and chances of sparking are less that's why we provide tap changer in primary side

Is This Answer Correct ?    1 Yes 0 No

Why TAP changer provided in primary side of HT transformer ? and why not in secondary?..

Answer / jayakumar

If only one tap changer is required, tap points are usually made on the high voltage, or low current, side of the winding to minimize the current handling requirements of the contacts. However, a transformer may include a tap changer on each winding if there are advantages to do so. For example, in power distribution networks, a large step-down transformer may have an off-load tap changer on the primary winding and an on-load tap changer on the secondary winding.


Reference from Wikipedia

Is This Answer Correct ?    3 Yes 3 No

Why TAP changer provided in primary side of HT transformer ? and why not in secondary?..

Answer / ram sumer

This depends on your use,for which perpose transformer is
been used. If the transformer is usde for long distance
transmission line i mean in delta to delta HT transformer
tap changer will be provided on primary side. To cover the
line losses which make a cause of voltage drop,when primary
side tap is changed in ratio of that tap position secondary
will also increase or decrease the voltage as you desire.If
you provide it on secondary side it will oppose the primary
voltage
But in case of distibution transformer i mean delta to star
tap changer is provided at secondary side.

Is This Answer Correct ?    4 Yes 14 No

Why TAP changer provided in primary side of HT transformer ? and why not in secondary?..

Answer / s hubertsubis

if you provide tap changer on ht side we variy the voltage
as we required at secondary side if we connect in secondary
side we can variy the current as the changes in load

Is This Answer Correct ?    10 Yes 31 No

Post New Answer

More Electrical Engineering Interview Questions

Is there any relevant technique to produce power from light and heat energy of the sun simultaneosly from same rays of light?

0 Answers  


how to select the automotive wire size by mathematical calculation. for xenon headlamp with ballast. the ballast given data voltage 10-17v,current permenant 6amp, run up phase is 15amp, peak at swicth on max 400micro sec is 40amp.the sum of cable resistance is 150mohm.please provide referenc document if any for relating the peak at switch on current,time & wire wire size

0 Answers   Tyco,


which motor is used in our Indian Ceiling fan -Capacitor start and run or Capacitor start? (during repair i saw only one capacitor so it should be start only)

5 Answers   ABB, Bajaj Electricals, Power Grid, Ruchi Soya, Suzuki,


what is voltage present between to phases in a three phase motor?

1 Answers  


why the generator efficiency is greator than motor?

4 Answers  


what is the power factor?please tell me uses.

5 Answers   NTPC,


TYPE'S OF BREKAR ,WHAT IS TRANSFORMAR & SAFTY. STARTER DOL & STAR DELTA STARTER.

0 Answers   Amtek,


what is the pressure in side transformer under normal condition?

1 Answers  


what is the voltage regulation constant of ACSR Raccoon conductor

1 Answers   KSEB, PSC,


what happens to the supply voltage if there is any change in frequency?

1 Answers   Gridco,


Short circuit voltage of a transformer mainly depend on A ohmic resistance of primary B ohmic resistance of secondary C magnitude of leakage flux D cross sectional area of core

1 Answers  


What will happen when we connect 2 bulbs in series between 2 phases

7 Answers   Pepsi, PowerTech,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)