What are the testing to be done before the installation of
1000 KVA Transformer?
Answers were Sorted based on User's Feedback
Answer / jyotirmaya
Normally test are done before installation and commissioning
of the transformer. The following test are done;
1. Visual Inspection
2. Insulation Resistance Test
3. Ratio Test
4. Vector Group Test
5. Magnetizing Current Test
6. Core Balance Test
7. Winding Resistance Test
| Is This Answer Correct ? | 38 Yes | 3 No |
Polarity Test also an important before loading
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / rajan singh tanwar(j.k. cement
For Power
Transformers the
following Pre
Commisioning tests
are done:-
1.Visual Inspection
2.Measurement of IR
Value
3.Measurement of P
I Value
4.Measurement of
Winding
Resistance
5.Short Circuit Test
6.Oprn Circuit Test
7.Magnetic Core
balance Test
8.Voltage Radio Test
9.Oil BDV & Acidity
Test
10.Checking the
function of
OTI, WTI, OSR, MOG,
PRV
Relays
Last one for the
relay's testing but
it also comes under
transformer testing.
Thanks
| Is This Answer Correct ? | 3 Yes | 0 No |
hou we find and calculate the maximum lode capesity of transforer?
what is the Excaste meaning of CT Saturation?? 10 P 20, 15 VA, what is the meaning of 10, & 20. if the CT polarrity changed what will happened?? what is the differece between measuring CT & Protection CT?? what is the Saturation Point of measuring CT & Protection CT??
What are the factors which influence the choice of specific magnetic and electric loadings of a synchronous machine?
what is the type of motor that is used in emu units in india
At what speed 1 HP motor can run an electric car of weighing 400 kg?
what happens when we apply dc to a transformer
IS RTCC AND OLTC REQUIRED FOR 500 KVA 11KV/433V TRANSFORMER FOR AN INDUSTRY?
7 Answers IGCAR, TNEB Tamil Nadu Electricity Board,
A double circuit with dog conductor 66KV Transmission line from wind farm evacuation to feeding substation having capacity of 25MW for transmission. Can same transmission network be considered for further expansion of Power & how much in MW. If we need to expand next 10-15 MW more will there any augmentation is required in transmission network? Kindly reply asap.
Find active & Reactive Power transmitted in a transmisston line having Vs30 degree(sending end) to Vr(zero degree)at receving end with line inductance X ohm. Vs(30degree)-------------------Vr(zero degree) X ohm
If Two Generators are working parellel in a network and suddenly the field of one Generator get weakened What will happened if there is no reverse power relay fixed in that Generator panel????
What is the difference between PLC and Embeded system
What are the conditions to be satisfied for parallel operation of dc generators?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)