If Two Generators are working parellel in a network and
suddenly the field of one Generator get weakened What will
happened if there is no reverse power relay fixed in that
Generator panel????
Answers were Sorted based on User's Feedback
Answer / g.bhardwaj
If two generators are working in parallel & no reverse
power relay installed then during weakened of field of any
gen set,definetly sick gen set work as a induction motor &
other gen set trip due to overload.
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / nishad
If there is no reverse power relay fixed, then it
definetely work as synchronous motor. if it work as the
same, it will affect the present network, because
1, It will draw the current from the other & will trip the
particular network system.
2,Already both generator working in parellel.so if one fail
the full load of the system will be the responsible of
working one. that's why it'll trip by over load.
3, If that field weaked generator work as a motor, it
defenitelt affect the primover ( Diesel Engine / Turbin)
there will be a chance of break down if it don't stop.
IF any another answer pls welcome>>> Nishad
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / lankesh
what you ment by field weakening Assuming field voltage is
reduced and another gen is having enough capacity, the weak
field gen wil deliver less reactive power as the mechanical
energy supplied is not reduced continue to deliver active
power
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
Less excitation?. Then the generator will continue share the
load at leading power factor resulting in higher armature
current as the prime mover is still running and the terminal
voltage of the Gen is reduced.If this current exceeds the
set value ,Gen will trip on OCR which does not allow for
very low pf.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.jeyvelraja
The weaked field get another set zero so that particular
gen worked not agenerator
Is This Answer Correct ? | 0 Yes | 2 No |
Answer / raju pohane
if in running condition one generator field wdg became weak
that time this generator will go in field weakening
position and speed will suddenly high and generator will
trip on over speed due to tripping in one generator, load
will shift on another generator and if there will no span
for load in another generator it will also trip.
Is This Answer Correct ? | 1 Yes | 3 No |
What is the difference between single core 2 wire and single core 3 wire system? Which application we are using this? and for What purpose we are using this?
What is purpose of APFC panel?
7 Answers Techno Electric and Engineering,
As load in a transformer increases, mutual flux linkage in core= A increases B decreases C not change D first increase then decrease
how to find out basic difference between ELCB,MCB AND RCCB on seeing the materials?
What is the name of powder which is used in inner side of a cable? and purpose?
give types of Air conditioners commonly used &its use?
what is frequency transformer?
Is there any problem ,if R-Y-B voltage is constant , but the air compressor taking one phase high current.what is possible causes.the said compressor is very new.(55kw).
I AM COMPLETED DIPLOMA IN E.E.E. AS WELL AS B.TECH IN ANDHARPRADESH.. HOW I THE Certificate of competency as Electrical Supervisor.
what mean by analog ,digital,numerical meters and relays? say the example?
which of the following is the earliest known literary source of ancient india and indeed of mankind
I would like to know that the fault curretn at base load and at 10% generation will be same? Fault level of BUS remain same with different generation?