how much Amp we can put in 1200kva generator?
Answers were Sorted based on User's Feedback
Answer / mohamed ali
Dear there are use the Formula
I= KVA X 1000/1.732 X 440 X 0.8
100 % - 1669 Amps
80 % - 1335 Amps
So always put in Amps 80% mean 1335 Amps
Is This Answer Correct ? | 8 Yes | 0 No |
Answer / mohamed ali.m
Dear there are use the Formula
I= KVA X 1000/1.732 X 415
For Example
1200KVA
1200x1000/1.732x415= 1669.4 ( Full load Amps
= 1335.5 ( 80% Load Amps)
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / a.bala
As per manufacture recommendation 80 % load can be
possible in continious operation mode . APPX 1300A
or
/ day hour basis u can load up to 100 % APPX 1700 A
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / deepak tyagi
KVAX1000= 440XIX1.732
I=1200,000/440X1.732
I=1574 AMP.
WE CAN DRAW THE MAX. CURRENT 1574 AMP.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / vijay
hey guys i think it depends on the power factor
if it is 0.9 then 1200kva*0.9=1080 kw
if it is 0.8 then 1200kva*0.8=960 kw
now you can use your formula
p=sqrt3*V*I*Cosphi watts
I=P/sqrt3*V*Cosphi amps
I=(1080/sqrt3*440*0.9)*1000=1576 amps for 0.9 pf
I=(960/sqrt3*440*0.9)*1000=1401 amps for 0.8 pf
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / vijayakrishnan
KW= KVA X PF
please don't include the P.F
I = KVAX1000/1.732XV
I=1200X1000/1.732X415
I=1669.49
now we will be take only 80%
so we take 1335A only
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / nikhil shinde
assume, pf=0.8
then
1200*0.8=960 KVA
I=kw*10^3/1.732*v
=1335.55 @100%
=1068.44 @80%
Is This Answer Correct ? | 0 Yes | 2 No |
can we start mulitple 3 phase induction motors with common starter?
what is the procedure for cable sizing or on what basis we will calculate the size of cable?????
cab we add capacitor bank with generator to improve power factor or not??????
Write down the classification of the transmission line?
definition of transponder?
Can anyone tell the proper diagram of star delta starter????
why stay insulator is not used with stay wire for 11kv Lines. Whereas it is used for LT lines ?
If u have Powergrid model question papers Please send to below mail ID rajutheprince@gmail.com
how to calculate energy meter multipling factor by ct & pt raitio
how to calculate the cable size depending on the amps?
How u can give the overload setting to any motor protection relay for a HT motors with formula and Example?
what is the differation bewreen kwh & fundamental kwh in electronic trivector meters