in our sub station why we step down firstly 33kv\11kv then
11kv to 430v. can we direct step down 33v to 430.v.
Answers were Sorted based on User's Feedback
Answer / prateek lau
yes it is possible to step down 33kv directly to 430v but
in that the turn ratio of the transformer would be large
and it will increase the size as well as cost of the
transformer.
| Is This Answer Correct ? | 29 Yes | 6 No |
Answer / devesh mishra
yes we can directly step down from 33/.433kv.
the lv side remains constant for 11 or 33kv & hv side
depends on load i.e,
for load upto 4 mva 11kv ht line is required,whereas
for load above 4 mva 33kv ht line is required.
| Is This Answer Correct ? | 40 Yes | 25 No |
Answer / cv raman
Genarally load centers are very away from the Generating
stations & scattered too.No of 11/.430KV SS are very high
compared to 33/11KV SS. In the view of construction cost of
the 33/11KV SS is high compared to the 11/.430KV SS. At
this condition , construction cost of 33/0.420KV is very
high compared to the cost of 33/11KV SS. If we propose
33/0.420KV SS in all load centers the no. of ss will become
very high and construction cost will be very high.
Technically we can go for strigh step doun but it is not
economical.
| Is This Answer Correct ? | 16 Yes | 4 No |
yes we can do it.
But it is not feasible since
1]feeder were design on constant current (44kV/11Kv-line
from nearest substation to distribution transformer)
2]Distributor lines designs for constant voltage(11kV/440V-
line from distribution transformer to home)
It is normal practise to have less flctuation at load end.
please revert back for any query?
Nilkanth--SIEMENS
| Is This Answer Correct ? | 16 Yes | 7 No |
Answer / paramesh dutta
Yes, it can be done and it is being done. There are many
such substations with voltage ratio of 33kV/0.433kV.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / gurucharan singh
because of LV circuit breaker current capacity limitation
upto 3 MVA. Can directly step down from any voltage level
to 415V. but 3 MVA only that around 3150 A in Aluminium Bus
bar or 4000A in cu. bus bar. that about 3.5 MVA.
| Is This Answer Correct ? | 12 Yes | 9 No |
Answer / anuj
Yes we can step-down the voltage directly from 33kV to 430V
but it is not feasible since transformers turns will
increase which will ultimatly increases the cost and
secondly laod centres are far more distance than the S/S
which will increase the LT line and eventually the losses
are more in LT line than the HT line.Therefore from S/S to
the load centres, HT lines are running and near the load
centre distribution transformer is installed.By this way we
can reduce the LT line and ultimatly the losses
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / ramesh
Generally we can step up high voltage to low
or low voltage to high voltage for a possible range.
which is balance for our economical stage
but technically it is possible the turn ratio of the
transformer would be large and it will increase the size as
well also differs cost of the transformer.
so that generation for 11 kv increases up-to level ll 750kv
11kv-33kv-66kv--132kv---400kv--750kv
step down as 11kv-440V- 230V-110V
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / bk
Technically it is possible to step down voltage level to
430V directly from any upper voltage level. However, our
power system network is connected to local power plant (may
be a CPP) that generates power at 11KV level. therefore it
is requred bring the network power voltage level to 11KV
for distribution purpose.
| Is This Answer Correct ? | 5 Yes | 4 No |
Answer / vrs rathore
Yes we can, but if our exixting system is workable for only
11kv and required capacity is more then 4000kva then we
have to take 33kv connection and after that it has to step
down 11kv for supplying our esisting system, which is
working only for 11kv/430v.
| Is This Answer Correct ? | 3 Yes | 2 No |
In a company the lines carrying 33KV but the load is below 10000Volts so we know that <11KV we can put 11KV lines but the lines are 33KV,..so how we can step down the voltage to 11KV with out erecting a substation
When testing an earthing connection, we use a 60 or 100 candle bulb with a phase connected direct from supply and the other wire to the new earthing provided.If the bulb glows then the earth is ok.Else earth connection is not Ok. So, why dont we can use all the home appliances taking a single wire from the phase and the return connection to Earth instead of return connection to neutral?
what is difference between earthingpits,earthing grid & earthing mess?
We have drive feeding an output contactor for a 5000 hp motor @ 5kV application. The motor FLA is 629amps x 1.25% service factor = 786.25 amps The cable that we current have in place between the drive and the output contactor is 350kcmil- MV-105 (parallel cables). Per the NEC table 310.60 (C) (69). This show the cable ampacity is at 615 amps per cable for a rating of 1230 amps. We have derated the cable for the cable tray and the multiple cables application and our calculations show that after the correction factor factor we are at 922amps. 1230 amps x .75% correction factor factor = 922.5 amps. The customer is driving us to then use another safety factor of .25% off of the already derated cable. Can you please provide a longhand calculation for your solution on this application?
when elecromagnatic waves are propogated in a wave guide?
The maximum demand of consumer is 2 kW and his daily energy consumption is 20 units. Its Load Factor is (1) 10.15% (2) 41.6 % (3) 50 % (4) 60%
What is mean by power factor?
18 Answers Shreem Electric Ltd,
How a capacitor discharge weld power supply works? what is the use of a pulse transformer?
what is difference b/w earth and ground?
what is the synchronous timer ? and it applications.
what is the cable size we can use for 11kv and 33kv ?
What is meant by sag?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)