how choose conductor &caple&wire depending upon the load
Answers were Sorted based on User's Feedback
Answer / ccic
Cable/wire , i.e. the conductor should be rated for at
least 125% of the FLA. The upstream CB protecting this
conductor should also be rated similarly, i.e. for a load
with 100A as FLA, the cable should be able to carry at
least 125 A. The cable derating factors (type of cable,
type of installation, ambient condicions, Voltage Drop etc)
should then be used to select the ACTUAL cable. The CB
should be rated for 125 A (Instantaneous Trip setting)
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / k.p.sharma
Size depends on two things
1. Current rating normally load current should be 70-80% of
cable's minimum capacity.
2. Voltage drop should be within limit i.e. for lighting 3%
and for motor during starting within 10%.
Is This Answer Correct ? | 4 Yes | 9 No |
Find active & Reactive Power transmitted in a transmisston line having Vs30 degree(sending end) to Vr(zero degree)at receving end with line inductance X ohm. Vs(30degree)-------------------Vr(zero degree) X ohm
how many earthing required for ups, what should be the earth voltages
What device is use for metering current at lt consumer end..??
which will glow brighter?bulb 1 (110v,100w) and bulb 2 (230v.200w) series connection
What is cable size of motor if starting current is 15.6 Amperes??
In India,we use 230V,50HZ,where as many other countries use 110V,60HZ what r d advantages and disadvantages of each of them?
A FIELD MAGNET IS EXITED BY AC/DC?
what happen to the voltage and current in all phases when an earth fault occur in a phase in three phase three wire system(delta connected)...
How to synchoronize the generator (with gcb,GT) to grid????? ????? from Grid iam getting power (rated 400kv/20kv) through GT and its goes to UAT.,,ST.,, now my generator(rated 20kv ) ready.,, now iam closing my GCB.,, in GT iam suddenly giving 20kv on that Gt.,, what will happend
Why we are measured insulation resistance applied through DC Voltage?
why any inductive load need free wheeling diode?
what is the different beetween kva and kwh?