parallel operation for tansformer which condition fill fil
for that
Answers were Sorted based on User's Feedback
Answer / siddikh
1.polarity must be same
2.phase sequence must be same
3.turns transformation ratio must be sane
4.frequency must be same
5.% Impedence must be same
6.Vector group should be identical
Is This Answer Correct ? | 19 Yes | 1 No |
Answer / irfan
1.polarity must be same
2.phase sequence must be same
3.equal voltage
Is This Answer Correct ? | 11 Yes | 6 No |
1.polarity must be same ( Must be full fill )
2.phase sequence must be same (Must be full fill )
3.turns transformation ratio must be sane ( Desired )
4.frequency must be same ( Must be full Fill )
5.% Impedence must be same ( Desired as to ensure equall
load sharing of both the transformer
6.Vector group should be identical ( Desired )
Is This Answer Correct ? | 6 Yes | 1 No |
following
1- KVA rating should be same
2- Voltage should be same and
3- frequency should be same
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / manoj tyagi
1. same voltage ratio
2. the per unit leakage impedence of the xer r based on
their own kva rating must be equal
3. ratio of eqv. leakage reactance to eqv. resitance should
be same for all the xers
4.transformer must be connected properly
Is This Answer Correct ? | 2 Yes | 3 No |
Answer / ashok
1)polarity will be same.
2)phase sequence must be same.
3) turns ratio will be same.
4)impedance will be same.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / vilas
1)Transformer primery voltage rating should be same.
2)phase sequence should be same .
3)polarity should be same.
4) Vector group should be same ,for example :dy11 etc.
These point to be considered while making parallel
operation of the tansformer.
Is This Answer Correct ? | 0 Yes | 2 No |
Answer / maneswar
1.polarity must be same
2.phase sequence must be same
3.turns transformation ratio must be sane
4.frequency must be same
Is This Answer Correct ? | 3 Yes | 6 No |
Answer / khalander mulla
to manage load at integrated steel plant to recover plant
load
Is This Answer Correct ? | 0 Yes | 4 No |
in our 6.6kv motor feeder[it is having two sources from Bus A&B] earth fault relay is acting, we checked CBCT connection and cable meggerd values found very good still earth fault acting during first two are three start after that it will hold. please clarify what was the reason. if same motor is starting from other Bus-A it will start.
whis is the formula of converting KW into HP ?
how we can calculate cable size of 230v,1 hp single phase motor ? panel to motor distance is 25 meter
What is the purpose of Vector Group in transformer?
1 Answers Andritz, ThyssenKrupp,
why characteristics of overcurrent relay is time-->psm instead of time-->current?
WHAT IS THE HIGHEST UNDERGROUND TRANSMISSION VOLTAGE IN THE WORLD?
What is the fullform of IPS in substaion using Aluminium Tubes
How to test the thyresitor or SCR by multmeter?
In a flange coupling, the flange bolts are designed for
types of motors suitable for escalators with reason
how a single machine can act as both motor and generator? and give explanation interms of connections?
how can i find ct ratio of meter by seeing name plate of meter and how it should be used in MF calculation if it shows only-/1???