if the back emf eqution for dc motor EB=(QPNZ/60A) THEN
what is the value of A for PMDC MOTOR OR how can dicide the
value of "A"
Answers were Sorted based on User's Feedback
Answer / gk
A= NO.of parallel paths related to type of winding.
IF machine is having wave connected winding then no.of
parallel paths are 2 always.
If it is lap connected A=no.of poles i.e A=P.
Comments and additions are welcome. TQ
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / vinod kumar
no of parallel paths for collecting current
| Is This Answer Correct ? | 0 Yes | 0 No |
Explain Even and Odd signals?
why fault current time duration is calculated for 1 minutes?
1 Answers Rockfort Engineering,
What are the causes for the failures of sandwich type (Al) busducts?
how to calculate the transformer losses.
why capacitor rating measure in KVAR. ?
why generaotr rating is in kva and dc motor in kw?
what is the effect if we add capacitor on DG supply, it has any loss or benefit.
What the capacitor Current formula?, For 1 KVAr how amps its required? for using the KVAr for boosting the PF Design Calculation.( Eg: for 30 KVAr required how many KW?)
17 Answers Alstom, Call Centre, EDC, HCL, Procon Engineers,
A 7 storey building has a floor area of 35,000sq.ft on each storey. On the ground floor 11KV electrical sub-station is to be erected. A load of 3kw for every 400sq.ft (p.f is 0.8) is proposed for each floor. fire pump 7.5hp, water pump 5hp, lift 2 nos, each 10hp and 20shop load of each shop is 5kw. calculate a. load each floor b. total load of building c. L.T feeders for aech floor and from transformer to main. d. distribution diagram e. capacity of sub-station/capacitor bank f. line diagram
if we look on phasor of the transformer vaoltage is 180 oppsite at primary and the secondary so to improve a power factor is secondary should kept negative to improve it primary side means is -.90 became +.90 at other side
why there is a 2 slits in three pin's earthing pin?
Three set (each phase contain 2 cable of 400 mmsq CU XLPE AWA) of single core cables are connected to 11 KV motor of 14 MW & the switch gear supplay is taken from 11kv feeder & this supplay taken from 275 KV substation. Problem is one pair cable(L3- 2 cable ) getting very hot & gland melted and damaged in switch gear side. the other two cable haven't any more hot(ambient temp only & L3 haveing 95- 100 Degree C. The same problem happened in 275 KV substation switch gear side also where the supply taken for 11 kv switch gear. But here L2 phese cable had problem. Why it is happening like this?. The cable having temperature different at different location from gland side inthe case of 11KV feeder of 275 kv substation. why ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)