When neutral is grounded in electrical circuit?
Answers were Sorted based on User's Feedback
Answer / abhiramsahu2007
FOR STAR CONNECTED CKT ,TO BALANCING CURENT THE NEUTRAL IS
GROUNDED
Is This Answer Correct ? | 28 Yes | 2 No |
whenever a live wire touches an enclosure of an equipment a
ground fault occurs, so to provide the personnel protection
the equipment enclosure is connected to grounded neutral
wire through a grounding conductor to make earth and
enclosure electrically common. At the same time the ground
fault current flows from the enclosure back to the source
to trip the protection device
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / saurabh
1) Neutral Shifting is Prevented.
2) System/Personal Safty increses
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / eduardo
There are 3 types of neutral systems: TN TT and IT. In both
TN and TT the neutral should be connect to earth. IT the
neutral should not be connect to earth (or connect via a
high value restistor).
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / gunasekaran
where it is sorce end and distribution level
Is This Answer Correct ? | 0 Yes | 2 No |
Answer / gunasekaran
if it is source end it should be another one is
distribution end.
Is This Answer Correct ? | 0 Yes | 2 No |
when you use input side delta-star txt
than u txt secondary u will connected the neutral and u r
load is safe and search voltage going to grounded.
Is This Answer Correct ? | 2 Yes | 5 No |
In three phase energymeter the spindle rotating backward why?
Is it required to use 2 nos of body earthings to any machine though if we use TP with E supply is provided to Machine?
Why the output of OP-AMP is always less than Vcc?
Why corona leads to production of Ozone and glow of the color VOILET?
how can we calculate ct ratings ?its any formula ?
what is the formula to calculate kva genset required for a given load in kw.
What is the difference between online and offline UPS
DIFFERENCE BETWEEN TRANSFORMER AND CURRENT TRANSFORMER?
why high speed tripping relay is used in protection circuit why not normal relay
there is a line fault some where on the ove head distribution line. how will i locate the fault for clearing it? ofcourse i have to megger the line but what information makes me clear that the fault is in that section of the line?
The cable area of cross section is 185 sq mm. How to convert this to the diameter.
how will you determine the short circuit capacity of a network