Befor synchronissation of Generator what test to be carried
out.pl.specify with reason.
Answers were Sorted based on User's Feedback
Answer / vijay
Before Synchronisation mainly three conditions
(voltage,speed/frequency & Phase sequence) has to be
checked which are within the limits. Reason to monitor when
any one on this parameters found not in unique, DG set's
not getting synchronised.
If the synchronisation happened in unconditional status, it
causes unbalance current will flow in the operation and
load sharring is not even. To eliminate this kinds of
occurence Dark lamp test was carried out before execution.
Is This Answer Correct ? | 9 Yes | 1 No |
Answer one is mostly correct. Two other factors are important. 1) the winding type (e.g. 2/3 or 5/8) as this can affect circulating neutral current. 2) phase angle at time of synchronising must be within limits to prevent high currents to pull DGs into synch.
For answer two - load sharing equipment can allow DGs of different ratings to be used in parallel. Frequency is important not RPM. The number of poles in an alternator can vary requiring a different RPM for the same frequency.
Another important factor iis governor response to load changes
Is This Answer Correct ? | 0 Yes | 0 No |
BOATH THE DG'S ARE EQUAL RATING(KVA)
BEFORE SYNCHRONISING THE TWO DG'S TO CHECK 1)BUS VOLTAGE
2) FREQUENCY 3) RPM
Is This Answer Correct ? | 0 Yes | 4 No |
How much depth we will take in 33kv sub station and why.
What is stepper motor?
What will happen if 33 kv is given to a 11/0.415 kv Distribution transformer?
How amny AH battery required for 600va inverter ?And how many hours it will give backup for ceiling fan ?
From an electrical motor & electrical generator, which has more efficiency & why?
how fault in an electric system is detected & hw protection of equipments is done ?
What is the function of retrip in busbar?
What is the difference between split AC and Casste AC?
what is load despatching
in the farm,water tank of 8000 litter capacity situated in 12 meter above.Farm owner want to lift 7000 litter of water within 7 minute to water tank of 12 meter above.which motor having HP rating is suitable for pumping??
1 Answers ABB, Anchor, Havells, Keltron, KSEB, L&T, vguard,
why generator and t/f ratings given in kva & motor rating is in KW?
A 11 KV motor is working. if the supplay is fail. what will happened with it's breaker? Trip / remain the same condition?