How to calculate the ups battery back up? give the formula.
Answers were Sorted based on User's Feedback
Answer / shailesh singh
Battey backup(va)=mah×v×n of battery/watt
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sathiyanarayanan
backup formula= KVA/DC LOW *POWER FACTOR
FOR EX:2 KVA/120 DC VOLT(SYSTEM VOLT)OUR MAINTAINED POWER
FACTOR (0.8 P.F),PER BATTERY=12V(DC LOW=10.8),HERE USING THE
SYSTEM VOLT=120V SO,10 BATTERIES-10*12=120V
DERIVATION : 2000/108*0.8
AH=14.81(APP.17 AH BATTERY) given 30 minutes backup
Is This Answer Correct ? | 7 Yes | 8 No |
Answer / chetan singh
Battery Volt X No of Battery X Battery AH / Load in watt
Is This Answer Correct ? | 4 Yes | 5 No |
Answer / mehboob
( Battery Voltage * AH Rating * Efficiency) / VA Rating = X
X * 60 = Estimated Run Time in Minutes
So let’s pretend we’re looking at a theoretical UPS unit that has the following specs:
VA Rating: 700
Battery Voltage: 12
AH: 9
Efficiency: 0.9 (90%)
When we plug those numbers into the equation we get the following:
( 12 * 9 * 0.9 ) / 700 = 0.139
0.139 * 60 = 8.3 minutes
Is This Answer Correct ? | 0 Yes | 3 No |
In a three-phase full converter, output voltage pulsates at frequency of a. f b. 2f c. 3f d. 6f
How i can decide that HVDC line is best for transmission.
what happen if the battery is charged by more than one source ,for ex: connecting data cable to laptop & charger pin to source supply ?
what is two wattmeter test
why inuctive drop is not consider in DC MOTOR
what is sinwave ups
what is the difference between PLC and embedded system
In ac circuit R,L,C are connected in series what is the output the circuit? explain
why we have to do tan delta test of the transformer oil???
Input power is 380 - 450 V but with 45 - 55 Hz frequency - desired output is 415 V and 50hz with 1% variation permissible. CVT / Servo dont stabilize the Frequency - what is best solution??
what is the use of capacitor bands?
what is neutral grounding resistor?