hi vishok this is noor plz tell me what type problems will
occured i use T/C in the place of RTD in (FEED WATER
TANK),plz send ur e-mail address to my ID
(mail2noor.hyd@gmail.com)
Answers were Sorted based on User's Feedback
Answer / bm
No problem will occur if you use T/C inplace of RTD.
However as the temperature in feed water tank is less, and
RTD has better linearity,accuracy in lower temperature,
RTD's are preferred over T/C.
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / solomon
No problem.costwise T/c better.accuracywise RTD better.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / g.ramki
hi noore use RTD for good in low temp application,feed wtr
tk temp max 100deg.rtd will give good accuracy if u want to
change u ave to lay tc cable.
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / arun
We use RTD in place of T/c because rtd have the greater
accracy in comparation of T/c.
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / goutam
Fine Noor ,you wont face any problem but in case of accuracy rtd is better than t/c and to that you need to do the connection as for an rtd.
Is This Answer Correct ? | 0 Yes | 0 No |
why k factor is important to know in flow transmitter. if we don,t know k factor what will be issue we can face .
1 Answers Flour Tech Engineers (P) Ltd,
units of pressure,flow, level,temperature? principle of pressure gauge? calibration of pressure tx., level tx., temperature tx.flow tx.? description of two wire ,three wire and four wire R.T.D.? WHAT IS INPUT AND OUTPUT OF TX.? WHAT IS INPUT AND OUTPUT OF R.T.D. AND THERMOCOUPLE? WHAT IS HOT LOOP AND COLD LOOP? WHAT IS INPUT AND OUT PUT AND OUTPUT OF D.C.S. AND P.L.C.? PRINCIPLE AND WORKING OF HART? WHAT IS PNP AND NPN PROXY? CALIBRATION OF PRESSURE ,LEVEL ,FLOW SWITCH? DESCRIPTION OF FIELDBUS FOUNDATION? WORKING OF SOV.?
In apron feeder how TPH is calculated?
If a transmitter is installed 10 m below its tapping point how much pressure exerted if fluid is water?
A valve in series with an orifice plate (DP transmitter), is aligned for constant pressure in the pipeline, if there is an error dx, How to align it in process.
what is Least Value of MICROMETER?
tion 0,50,100% equql to voltage formula?
How can a d.p. Transmitter be calibrated?
Transmitter reading is zero but in DCS showing one Bar what is the reason ?
How is plc installing done
how will you segregate the alarm levels in alarm management system during factory Acceptance Test
how to calibrate 0- 150 psi presure gauge by dead weght tester