HAI,HOW TO SET THERMAL OVERLOAD RELAY FOR DOL STATRTER
FEEDER AT START AND RUNNING?
Answers were Sorted based on User's Feedback
Answer / fairos
First, for thermal overload relay has no meaning in term of setting it while on running or starting. It purely based on rated current of the motor.
when you look at the nameplate of the motor there should be a data that mention "duty" which normally either 1, 1.1 or 1.2 in value. If the duty is 1 then you can only set the overload relay at 100% of the rated current. If duty is 1.1 then the motor is allowed to operated at 10% higher than it rated current hence you can set your relay at 110% of rated.
Generally people would set at 10-15% higher than rated current. But sometimes being conservative is okay, which you can set the relay below the rated current. This can be done as long as it is not tripping unnecessarily.
Is This Answer Correct ? | 22 Yes | 3 No |
Answer / vilas
First take a current of each phase with tong tester,while
running on normal load,
Then set the over load accordding to the load slightly
higer than normal running current, care should be taken
that it should not be more than rated current which is
always mentioned on the motor name-plate.
Is This Answer Correct ? | 7 Yes | 7 No |
Answer / pankaj sharma
Set the relay to motor full load current as mention on motor plate
Is This Answer Correct ? | 5 Yes | 5 No |
Answer / mohit
set thermal overal relay to 95% of full load current of
motor.
Is This Answer Correct ? | 6 Yes | 20 No |
how many load we can take for lighting
where does core based current transformer is used? and what is the value of lux in a work station?
what is the difference between the voltage of 5 volts capacitor and and 5volts battery?
what is diffrent between plc and clc??
can we use HPSV LAMP in HPMV LAMP fixture ?and viseversa.
Whether amorphous core transformer is available in India?.If available then up to what rating of voltage and KVA?.
0 Answers DAE, Tata Chemicals,
please I wont know how to calculate the vector group for power transformer ZNyn11 best regard.
the max. power will be transferred if …… a) sending end vol. is high b) receiving end v is high c)…….. d) corona loss is least
2 Answers Engineers India Limited,
why wound rotor is star-connected?
What is EPBX????
i have 60Hz motor, can i run it at 50Hz power supply ???
why fuse is not applicable for nutral and what will happen when it applied.