For 415v,3phase,22kw rating of motor how to calculate MCCB rating
Answers were Sorted based on User's Feedback
Answer / ucmed_king
Refer Manufacturer coordination chart for required rating and model of MCCB.
There is a thumb-rule though. Convert KW to HP (KW/0.75), multiply it by 1.5 gives you the rated current. Multiply it by 1.5 for breaker value.
Here's the coordinartion chart:-
http://powertips-elec.blogspot.in/2010/11/selection-charts-for-dol-starters-l.html
Is This Answer Correct ? | 9 Yes | 1 No |
Answer / akash
39Amp Per Phase is the actual load, but you can be on safer using side using 50/63Amp MCCB.
Is This Answer Correct ? | 6 Yes | 0 No |
How to calculate the phase to phase clearness of HT /// LT bus bar?????
what happend if we remove dc exciter from moving machine..: gg
Transformer rating=> 15/20 MVA.Why there are two raings? What should be the rating of the fuse at the secondary if the voltage level is 13.8KV/4.16KV?
Why neutral shows voltage with earth ?
7/20,3/20 electrical wire is specified as stated.Why?
what is the meaning of "i.p.-43" and duty cycle-s1 on the name plate of a asynchronous machine?
what is parellel power factor correction?
What is the formula to calculate the rating of a thermal over load relay
In my power station 220 volts dc battery set. they coneected 84th cell taped
what are the types of sus station ?
Why we used 690V in ACS 800 drives.Why dont use standard voltage like 415v or 1.1Kv
If two transformers same rating(11KV / 440V)connected in the same primary line(11KV), can we connect(bus coupler) secondary side directly or need a synchronization????