Tell the details of the precommissioning tests that are
performed on distribution transformer, power cable and
switchgear (11kv).



Tell the details of the precommissioning tests that are performed on distribution transformer, pow..

Answer / subaharan

first check the transformer bushings and their condition,then
you meggering the transformer each phase to phase and phase to
earth.
power cable you check the high voltage test which is used for
measuring the leakage current,meggering and continuity
checking.
switchgear the same meggering,isolator checking,relay
testing(set various values of currents,voltages and set time
for tripping) make the fault and note the trip time.

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

1.two coupled coils with L1=L2=0.6 H have a coupling coefficient of k=0.8 the turns ratio N1/N2 is......

5 Answers   BSNL, SSC,


What are the layers of protection over armoured cables?

3 Answers   Accenture, IOCL,


please tell me formula of 3 phase induction motor under condition{1]when we 3 phase motor starts without load in star or delta connection?thanks

1 Answers  


what is the instrument used for measuring insulator RESISTANCE

5 Answers   TATA, Transco,


why we are not earthing ht cable at both the ends(sending & receiving end)?

5 Answers   Essar,






What is the bundle conductor?

0 Answers  


all 3 current transformers (C.T) are burnt in a L.T Panel - what are the possible reasons

5 Answers  


Explain in details how you would react to an unexpected incident when your supervisor or manager is not around to give instructions?

1 Answers  


how the vaccum ckt breaker workes..? how the arc is quenching in it?

1 Answers  


the voltage per turn of a primary winding of a transformer is the same as the voltage per turn of the secondary winding of the transformer. why?

8 Answers  


if i have 5kw,9A,three phase induction motor,if i want to install it 100 meter away from its feeder,how i will culculate cable size for this load.

2 Answers  


what is the generator rating for 40 amp load of 3phase motor.?? 400v voltage of generator... plz tell me with formula its urgent...plzzz... and also tell me that this 40 amp at all phases mean 40 amp on red,40 amp on yellow,40 amp on blue...... or the total sum of that 3phase is 40 amp....

7 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)