When charging a 20 MVA , 33kV/6.6kV transformer through
regulated (0-6.6 kV or 0-33 kV) source on no load , what
will be the maximum current drawn by transformer from
source and what sould be the source capacity.
Answers were Sorted based on User's Feedback
Answer / dinesh lokhande
Actually above answer is not correct as it is the full load
current.No load current is approximately 4 to 5 % of rated
full load current. hence considering the terminals (i.e HV
side or LV side) the current drawn from source will be 4 to
5 % of respective side rated current.
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / satya
the charging current is about 6 times the full load current
about 2000 amps but that will be for mill seconds
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / gunasekaran
for good transformer it should be 0.5%of full load current
for normal it may be upto 1%
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / pulkit
max current when on load wil be 390 amp drawn by the Hv wdg
of t/f and when on no load the transformer primary losses
occur on the basis of elctic flux principle in which when evr
the current flows in a loop,there is loss in the form of
magnetic field energy that is created arround the primary
coil.it is 1 % of the hv wdg current.
| Is This Answer Correct ? | 0 Yes | 0 No |
can a motor acts as a generator
ROC converges if poles and zeros lie inside a. Origion b. Z=1
we change the speed of the synchronous motor by incresing or decreasing a rotor resistance
why do power factor in the three phase induction motor increases with the load ???.
stand by earth fault protection (51G) for transformer rating 2000 kVA,Dyn11,33/0.400 V. LV NCT ratio and necessary resistor and metrosil values how to calculate
What is the difference in calculating size of AC cables compared to calculating size of DC Cables? Usually DC Cables are larger than AC Cables although they have the same ampacity. Why is it?
types of arc quenching methodes
How time response of the system is divided?
what is real and reactive power?
what is the diffrence between current transformer and voltage trasformer
Between Star-Delta & Star-Star Power transformer which one is efficent for Earth Fault?
Why not LED burn after showing alarm,as Alarm volt is 11- 13,But LED is of3 volt,why it isnt Burn??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)