What are the advantages of star-delta starter with
induction motor?
Answers were Sorted based on User's Feedback
Answer / k.senthil kumar
1. The main advantage of using the star delta starter is
reduction of current during the starting of the
motor.Starting current is reduced to 3-4 times Of current
of Direcr online starting.
2. Hence the starting current is reduced , the voltage
drops during the starting of motor in systems are reduced.
Is This Answer Correct ? | 132 Yes | 15 No |
Answer / sonu kumar
The main advantage of using the star delta starter is
reduction of current during the starting of the
motor.Starting current is reduced to 3-4 times Of current
of Direcr online starting.
Hence the starting current is reduced , the
voltage
drops during the starting of motor in systems are reduced
Is This Answer Correct ? | 53 Yes | 15 No |
Answer / amrinder singh rajomajra
The main adventage of using star-delta starter for
induction motors is as following-
if we start the motor with DOL(direct on line) or simple
starter the the motor requiers more current to start ,
which is 6-8 times the full load current.because the higher
tourqe is require to start the motor...
so in star-delta the motor is started in star, which
produce higher tourqe at lower current, means the starting
current is 4-5 times less than delta starting.
and then motor after start gets full speed and star
contecter is disconnect and motor runs in delta
connections.because torqe is less and lower current is
required.
Is This Answer Correct ? | 34 Yes | 6 No |
Answer / mohanraj
1. The main advantage of using the star delta starter is
reduction of current during the starting of the
motor.Starting current is reduced to 3-4 times Of current
of Direcr online starting.
2. Hence the starting current is reduced , the voltage
drops during the starting of motor in systems are reduced.
Is This Answer Correct ? | 23 Yes | 5 No |
Answer / partha
How the current is being reduced to 1/3 times in star/delta
starting. Can you please show it by derivation.
In my views power is reduced by 1/3 times and current and
voltage by 1/root 3 times. pls correct.
Is This Answer Correct ? | 14 Yes | 6 No |
Answer / jishnu mukherjee
The main advantage is of-course the issue of starting current.In this case the starting line current is reduced to one third.Most importantly, starting torque is also reduced by the same amount.So pumps,motor-generator sets, where starting torque is not required to be high can take the advantage of star-delta starting.
But the problem is, this method is not adoptable for the motors which have high voltage rating(generally above 3kv).The reason behind:such motors are usually star-connected.We must have delta connection in the induction motor.
Is This Answer Correct ? | 7 Yes | 3 No |
where lt & ht capacitor used
I am abt to give IOCL intrv.Plz sir guide me for IOCL intrvw (Electrical).Which subject to be consider. questions are generally asked from which subject.Plz help me out.
According to general circuit diagram of 1-Phase t/f , why the primary is not get short circuited ,even though the supply terminals both are directly connected through primary winding?
How to calculate the KA rating for a circuit breaker if we know the KVA rating of the generator feeding it?
I have 2500KVA transformer delta/star,13.8KV/380V provided with LV 4000A breaker. Already I have 2300KW motor feeder with a full load 90%. Is it possible to connect another 1600A from that breaker? If so how the calculation is done?
Can we use the Poly Phenly Sulphide instead of Poly Phenly Ether? Do clarify your opinion.
what is the standard duration after failure EB power
Which level of the Transformer oil got dielectric strengh? And why?
in ct secondary one terminal is connected to earth why?
Instead of single phase(220), if we apply Phase to phase (R&Y)supply (eg: for lighting fixture). what will be the power formula?
how to calculate sizing of NGTR (Transformer rating,Loading resistor value and Current rating of resistor) and what is the X/R ratio. Details : 11kV,Capacitance 1.73532 micro farads,40kA for 1sec.
1 Answers Bhel, Indorama, Power Grid,
how much excitation voltage required to generate 1mw power?