define IDMT relay?
Answers were Sorted based on User's Feedback
Answer / nimish
It is an inverse definite minumum time relay. In IDMT relay
its operating is inversely proportional to fault current
and also a characteristic of minumum time after which this
relay definately operates.
Is This Answer Correct ? | 250 Yes | 22 No |
Answer / klm
It is inverse in the sense , the tripping time will decrease as the magnitude of fault current increase.
simply saying,
"for a fault current of 25KA-the time delay may be 2s.
& for a fault current of 30KA the tme delay may be 1.5s.thus as the fault current increases the time delay decreases.
Is This Answer Correct ? | 163 Yes | 6 No |
Answer / suthan prabhu
It is Inverse Definite Minimum Time Relay. This will work
inversly proportional to Fault current and our time delay
settings in the relay.
Is This Answer Correct ? | 84 Yes | 20 No |
Answer / prasanna
IDMT - Inverse Definite Minimum Time lag
Inverse - Operating time is inverse with fault current magnitude
Definite - Time characteristics is definite (Near constant) irrespective of current magnitude
Minimum time lag - time taken to operate is less when compared to other protection relays
Is This Answer Correct ? | 52 Yes | 8 No |
Answer / md.moazzem hosen
IDMT relay means inverse definite minimum time relay.That
means when fault current increases then operating time
decreases.
Is This Answer Correct ? | 41 Yes | 7 No |
Answer / er. mohammed yusuf fahad
The IDMT Inverse definite minimum time relay is one such
type of relay where the delay time of the relay is
inversely proportional to the magnitude of the fault
current. For ex. If the fault current is of the magnitude
of 8KA the delay taken by the relay to tripp the ckt may be
3 sec likewise if a fault current of 16KA persists in the
system the IDMT delay time will automatically reduce to 1.5
sec and so on. It is used in applications of overcurrent
relays and earth fault relays.
Is This Answer Correct ? | 22 Yes | 0 No |
Answer / shyam
it is a type of inverse current relay but with minimum time
delay
Is This Answer Correct ? | 37 Yes | 16 No |
Answer / adesh
is an inverse definite minimum time relay
there are 2 precautions to be considered when using this these precautions are the time setting and the current tap setting
these are to be considered since the relay is dependent on the inverse of time
Is This Answer Correct ? | 22 Yes | 5 No |
Answer / n.ravi teja
it is inverse definite time relay.and in the name it self
inverse means when fault current is more then its operating
time is less.because if it takes more time the equipment
may damage.so to avoid this the relay is made with inverse
characteristics.
Is This Answer Correct ? | 12 Yes | 4 No |
If DG runing time neutral is disconnected what will be the effect in Engine and Electricial panel.
what is form factor?
A TRANSFORMER 440/400V,DELTA/STAR CONNECTED.THE NEUTRAL CONNECTED WITH GROUND CABLE THAT IS DIRECTLY CONNECTED TO THE PANEL,FROM PANEL IT IS CONNECTED EARTH PIT.IS IT RIGHT? IF IT IS RIGHT LEAKAGE CURRENT AFFECTED.SECONDATY IS PROTECTED WITH EARTH LEAKAGE RELAY.
how to commissioning the genset with amf panel?
What do you mean by cold shinkable cable joint.How it is done.
What is electrical grounding?
What are the commercial names of overhead conductors used in India?
what is the purpose of the armored for the power Or control cable? How to select the type of the armored?
in HT service 3ph 4 wire service Y-phase voltage shows zero . whether it is meter fault? or what be the reason ? if y-ph voltage zero ,can current is recorded? reasons for failure?
What is the difference between relays and contactor construction wise?
Why is DC use instead of AC for protection and control circuits?
Why we are not using capacitor in line when load on Genset?