Answer / sunil kumar
Before using 4 - 20 mA all most of the instruments were
using 0 - 20 mA but after some problem faced for
finding "live zero", it was changed to 4 - 20 mA. By live
zero I mean when the instrument is connected but with 0
process value, the current is 0 mA, & the same current
value is seen when there is a cable damage or no power. By
this it was difficult to find the live zero. After that it
was changed to 4 - 20 mA. 4 - 20 mA Why? why not 5 to 20 mA?
The reason is that most of the a to d convertor which is
capable of providing 1 - 5 VDC with 250 ohms the same
current could be used as per below.
4 X 250 = 1 V DC & 20 X 250 = 5 V DC.
| Is This Answer Correct ? | 78 Yes | 8 No |
Answer / gurpreet chahal
we use 4-20 ma to achieving maximum linearity ,and another
tning safety point of view no spark can genrate up to 20 ma.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / therion
for eg. if we are monitor a flow tube and measure the rate
of flow through the tube or pipe then 4mA will represent
ZERO flow and 20mA maximum flow..if it drops to below 4mA
then it shows reverse flow (which is not good)
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / sandeep bisen
due to achieving maximum linearity in between 4- 20 ma.
| Is This Answer Correct ? | 9 Yes | 11 No |
actually for plc and for electronic systems we usually
supply in mamps. GENERALLLY FROM TRANDUCER WE USE TO TAKE
OP IN 4-20MA , for RTD also .
| Is This Answer Correct ? | 4 Yes | 9 No |
why transformer ratinh is in KVA????/
8 Answers Apollo, Priyadarshini, Reliance,
why electrical power has benn needed for speed controller of woodward governor control for biomas power plant
what will be the breaking capacity of MCCB of 1000kVA (6% Impedence) transformer? Voltage being 415V, Power Factor 0.8.
which surface is suitable for NEUTRAL GROUNDING ?
please send me last 5 year interview questions
what are the types of transformers
how to apply b license to c license in tneb
why generally transformer are in star to delta
Do you know what is dry-out test in x'mer
0 Answers First American Corporation, GPSC Gujarat Public Service Commission, Jindal,
For a 6.6kV Motor it is recommended to do megger test with 500 V d.c and not more than 5kV d.c but the Hi voltage withstand test should be performed by 12kV AC. Why the dc voltage test should be limited but AC voltage withstand test could be with such a high voltage?
HOW DO A DISTANCE RELAY SENSES THE FAULTY ZONE.
how we calculate size of exciter(excit. volt and current) for generator?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)