HOW DO A DISTANCE RELAY SENSES THE FAULTY ZONE.
Answers were Sorted based on User's Feedback
Answer / amit sharma
distance relay operates on the zone impedance. If impedance
seen by the relay in the zone is less than the rated imp.
then relay trips and the zone is isolated.
| Is This Answer Correct ? | 16 Yes | 1 No |
Answer / d ramesh
Distances relay senses the faulty zone if impedance seen by
the relay is below the set value then it operates and
isolates the faulty zone.
z=v/i below the set, then operates
zone1= 80% of protected line
Zon2=100%protected line + 50%shortest line
Zon3= 100%protected line + 100% longest line.
| Is This Answer Correct ? | 12 Yes | 3 No |
Answer / sukhvinder
relay works is ratio of voltage over current.line is
divided into zones zone 1,2,3. zone1 is 80 per of line and
set for immediately trip for line
| Is This Answer Correct ? | 12 Yes | 4 No |
Answer / limbian
Distance Protection Relay senses the faulty Zone by
recieving signal from Voltage Transformer
| Is This Answer Correct ? | 1 Yes | 5 No |
Answer / j.kesavan
it is sense sending end receving end voltage relay trip
depending upon voltage.
| Is This Answer Correct ? | 5 Yes | 24 No |
What is frequency?
What is difference is of VSD,VFD,VSDS, are they the same as the direct current to control dc using above mention
The neutral to earth connection in my industry is showing a zero reading (shorted). I have a machine which has to be installed where neutral to earth is not shorted and shows a leak voltage <3 Volts. Please suggest me how it is possible.
why the electrical plug point pin(earth) size in max
1 Answers Autoneum Nittoku, Bajaj,
considering the 3phase and single phase ac system the load applied and the volage given is same...will the current differs for both the cases are it wil remain same?
why we using capacitor in single phase motor ?
difference between generator and alternator
if transformer winding burn on dc supply then why not alternator rotor winding please post answer on y.sakhare@rediffmail.com
why h parameter are called as hybrid parameter?
In Air circuit breaker LSIG protection unit is used. Without fault in cables (2 runs 3Cx150Sq.mm Copper, 1Kv grade, XPLE armored cable IR value is more than 550Mohm @ 500V Megger) and load section Long time Overcurrent protection is triggers and trips the unit. We changed LSIG protection with new factory tested unit. Even then fault is persisting. Please suggest the possible causes
Dear sir, By which formula u can calculate for a particular kv line there is a range of mw.
List examples of current sources?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)