what is the effect of power factor on DG supply,i mean to
say what will the effect if we add capactors on dg supply.
Answers were Sorted based on User's Feedback
Answer / sachin
there will not be an effect on DG if we add the capacitor.
But normally we recommend to install capacitor bank where
load is fluctuating, unstable.
Is This Answer Correct ? | 6 Yes | 3 No |
Answer / mahavir jagdev
The capacitor bank is kept to improve the power factor as most of the industrial load is inductive, hence to get the power factor to close to 0.85 or more the caoacitor bank helps. thus reduing losses.
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / praveen yadav
yes we can, but it can be upto safe life limit of extent of 0.95 P.F Usually dg set are designed over 0.8 P.F.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sumanth aptransco
idon't no about DG.in dc supply has no pf (unity).suppose we
connect c in dc it acts a open ckt.
Is This Answer Correct ? | 1 Yes | 5 No |
Why induction motor overheated?
2 Answers HVCC, Physical Research Laboratory (PRL),
How to calculate the CFM to TR? What is the Formula
Why temperature rise is conducted in bus bars and isolators?
what is meant by IGBT how they differ from tyristor ?
why lightning arrester and other equipment earthing conneting from same earth bar ?
How the output,losses and temperature of machines varies with linear dimension?
whats the differece between Exd and Exe
What is the difference between Generator Differential Relay and Transformer Differential Relay?
what is the diffrence between capasitor and battery?
What is true sine wave or pure sine wave inverter?? Is it sine wave or step wave?? If it is step wave, waves with how much step is considered as pure sine wave? Is it possible to produce pure sinewave using power electronics?
How to calculate the cable size (XLPE)for suitable to 120KW load (if Motor or heaters etc)
Acually generator neutral is earthed,if suppose cable from neutral is brokened under theearth ,what will happen.