how much amp MCB is required for 1/2 kva power back up?
Answers were Sorted based on User's Feedback
Answer / shantanu
Look 1KVA = 1000VA
Therefore 1/2 Kva = 500va
For a single phase current
500/230=2.174
So the MCB you can put here is a 2.5AMP as it will not be possible to get a exact 2.174amp MCB
Hope this solves your query.
Is This Answer Correct ? | 6 Yes | 3 No |
Answer / vicky
1KVA = 1000VA
Therefore 1/2 Kva = 500va
For a single phase current
500/230=2.174
So the MCB you can put here is a 2.5AMP as it will not be possible to get a exact 2.174amp MCB
Is This Answer Correct ? | 2 Yes | 0 No |