how to check the earth resistance value& what is the
minimum earth resistance for good earthing sysytem.
Answers were Sorted based on User's Feedback
Answer / jaydeep parmar
value of the earth pit should be less then 2 ohm and earth grid value should be <1 ohm
Is This Answer Correct ? | 427 Yes | 59 No |
Answer / tauseef tarique, engineer(e)
The earth resistance value can be checked by the use of
earth resistance tester (called megger earth tester). The
best earth resistance should be less than one ohm but the
permissible value is less than 5 ohm. For rocky areas it
should be less than 8 ohms.
Is This Answer Correct ? | 318 Yes | 43 No |
Answer / pandiyarajan
Grid resistance value should be lessthan 1 ohm
Is This Answer Correct ? | 209 Yes | 31 No |
Answer / aruna devi
By using earth megger .It should be less than 2ohm.
Is This Answer Correct ? | 227 Yes | 72 No |
Answer / bhavini
earth tester use for measuring resistance of earth pit
should be less than 1 ohm.
Is This Answer Correct ? | 105 Yes | 26 No |
As such there is no any standard of earth resistance value,
Its varies on different type of soil resistivity. Idley it
should be 0, but in different kinds of soil for electrical
equipment it should be better to below 10 Ohms and for
electronic equipment it should be better to below 5 ohms.
Is This Answer Correct ? | 100 Yes | 28 No |
Answer / ramaraj.g
The earth resistance value can be checked by the use of
earth resistance tester (called megger earth tester). The
best earth resistance should be less than one ohm but the
permissible value is less than 5 ohm. For rocky areas it
should be less than 5 ohms.
we using the DMM in check the L - N , N- E ,E- L
this small calc
L-N - 230 v
N-E - BELLOW THE 2 VOLTS IS GOOD ERATH CONN
E-L - 230v IS RECONFORM TO GOOD EARTH OR NOT
L-N = E-L
Is This Answer Correct ? | 77 Yes | 11 No |
Answer / bk sharma
It should be near <0.5 ohm for good earthing.
Is This Answer Correct ? | 64 Yes | 11 No |
Answer / bhanu
earth testers are used. and it is checked wheathe earh
resistance range is from 1-2 ohm or not.
Is This Answer Correct ? | 83 Yes | 39 No |
I have 480V Single phase and I am trying to figure how big of a transformer (KVA's) and Primary breaker size I need to provide 200 Amps at 240V for a building.
why motors are rated in HP?
from 33kv to 440v 2mva transformer how much full load current will be at ht side and lt side and which range of ctpt will be used?
How to calculate the current carrying capacity of electrical cables
16 Answers Barqaab, Grasim, Havells, HM Cables, Janapriya, Polycab,
how to calculate busbar capacity for 1000Kva transformer having22/.433V
2 Answers Electrical Tech, L&T,
what are the interview question asked in wind mill about electrical
how to calculate the bus-bar size. give formula with description
what is the proximity & ferranti effects can you explain to me
What is difference between earth leakage relay and restricted earth fault relay ?
if acapacitor connected to power supply will it cosume power& will it going to get recorded in energy meter
what is meant by boost charge in batteries
why core is useful for the transformer and in its operation