Answer / nishant
For staring of Motor above 5 HP we need a starter with
overload protection e.g. Star-Delta Starter and D.O.L.
Starter for limiting starting current as motor takes 5-7
times of its full load current during starting So if we
start 20 HP motor Directly the line fuses will Blown Off
due to high starting current.
| Is This Answer Correct ? | 19 Yes | 6 No |
Answer / sdr
Dear readers, you may please note that Induction motor of
any size can be started directly-on-line provided that the
system in which it is connected should be healthy enough to
keep the system voltage steady at the time of starting.It
is not at all deirable to use a starter if your system is
healthy.In practice ,we usally don't know how much our
system is loaded,so be at a safer side, we use starters to
start Inductin motors.Thus starters limit the high inrush
current at starting & keep the system voltage almost steady
to let peform the other machines steadily.
If a 20 HP motor started in star & kept continuosly running
in star, it will run but the capacity of motor will reduced
to 57.73percet of the rated one.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / mallikarjuna
Dear all readers so that if we 20hp motor start directly in
star nothing will happen and starting current will
less,suppose if connect to the motor in DOL starter the
starting current is 5-6 times full load the starting
current is around 150 amps ,when we connect to the star the
starting current is 60amps
| Is This Answer Correct ? | 3 Yes | 5 No |
Answer / ramya
above 10 hp we required starter bcoz, during the starting
of the motor ll get damage due to over starting current,
over voltage, increase in winding temparature,
thus to controll those faults we need decrease in starting
current, thus we run the motor with the starter. the name
itself indicates that it is uesd to start the drive or
motor.
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / hari
DIRECT STARTING WITHOUT STARTER IS POSSIBLE FOR DOL type
windings only,not for double cable motors.sudden load will
effects the transfomer and other electricl accessories.
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / dharmesh doshi
motor have no any problem to run but power consumption is high due to low power factor.
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / umesh
whenever we starts the 20hp motor directly with the mains
then its winding will be burnt, because the motor winding
have less then 10ohms, whenever current flows though the
winding the current will be 5000A, then it will be burnt.
that's way we use the starters for safty.
| Is This Answer Correct ? | 2 Yes | 5 No |
Answer / brijesh soni
If the motor strrted ok but if any Problem during at the
running as single phasing, over lodin, the motor will be
never Trippd but it will be Burn out
| Is This Answer Correct ? | 1 Yes | 5 No |
Answer / amit kumar
In this case , it delivers only one third power of the
rated capacity of the motor.
| Is This Answer Correct ? | 2 Yes | 7 No |
Answer / er.nitesh
Nishant is right but i want to say above 5 HP we use Star
delta starters and below it we use D.O.L.
| Is This Answer Correct ? | 0 Yes | 5 No |
why transmission is only 3 phase and not 2 or 4 or poly phases
star delta starter control wiring diagram?
ELCBs are installed for protecting humans from AC leakage current.Is there a device which protects humans from DC Leakage current??e.g.leakage from batteries...If not,then why so???
when power transformer is flashed which gas is produce in side?
What is the meaning of electricity? How it is being produced? Can we store the electricity? When we produce electricity what is the capacity of voltage current we are getting? If we need 440 volts how to get it? In case, if we want lower than 440 volts how to change it? Please answer?
If the soil resistivity is more large, how can we earthing our 11 k.v. transmission line?
Hot Water System (HWS). Will a 30ma elcb have more nuisance tripping than 100ma elcb
hi pot test principal
Can u explain : how capacitor act when the supply is given is a.c and d.c. I know that when d.c supply is given then the capacitor charges and becomes open circuited. But please say about when a.c is given. I have seen that when a.c supply is given ,it charges and discharges, But when we plug in capacitor to our daily supply and take it out ,then we join those wires spark will appear,which seems charge is present ,but when a.c is given it should charge and discharge
what is the Auto Mains Failure Panel function in DG?state its function?
why voltage drop if we have connected 230 v ac suplly through diode to bulbe we found haft ie 110 voltage drop why it is
how to calculate current carring capacity of cable and cable selection? 1) copper flexible cable 2) copper armoured cable 3) Aluminium cable
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)