What is transformer break down voltage.And what is flash
oil flash point.
It is transformer oil dielectric breakdown voltage.
A sample of the tx oil is collected and tested with a
special tester. In the tester is a pair of electrode spaced
as per BS
spec. A TEST VOLTAGE IS APPLIED ACROSS THE ELECTRODES , and
this voltage is gradually increased until a breakdown
happens resulting in sparks across the electrode, immeadetly
the test voltage is stoped and the RMS voltage is
calculated.A few test is carried over and the mean voltage
is taken as the breakdown voltage of the sample oil under
test.
It is flash point of oil.The flash point is at what temp the
oil would self ignite. This depends on the quality and type
of oil.
Is This Answer Correct ? | 2 Yes | 0 No |
Actually why the transformers are rated in KVA.?
Why transformer neutral is earthed
Dear All, In a 400V power system, ratio of three current transformers installed incoming switchgear is 4000/1. Maximum three phases short circuit current of this system is 48kA. One CT is installed on neutral of upstream transformer (6/0.42kV, solidly earthed) for 51G protection. Would you please inform me about the correct CT ratio of this current transformer (on neutral)?? Thanks a million
How the soft starter control the starting current in three phase squirrel cage AC Motor?
why we use star and delta connection?why we donot give the supply directly?
12 Answers Hitech, Siemens, Tata Steel Limited,
When will you multiply and devide with derating factors to the actual value while sizing the cable?
what is the 2MVA distribution transformer efficiency
How can you measure battery AH?
If current flows through conductor it produce magnetic field only.but if current flows through vaccum both magnetic & electrical field produce why ?
what is the difference between single phase, 2 phase, and 3 phase in electric meter?
how to select the mpcbs and contactor for 3 phase 30 hp star delta motors.for plc control.and tell me the calaculation for future use.
What is R/X ratio? I have heard that this ratio is higher in a radial distribution system.Why is it so? I would appreciate a word. Thank you
1 Answers Power Grid, Vignan University,