What core magnetic balance test of transformer?
How to do this test in a three phase Star delta (star-LV,
Delta-HV) transformer?
How to measure and where to measure?
thanks and regards
Austin
Answers were Sorted based on User's Feedback
Answer / mustafa
This is nothing but voltage ratio test, To find available
voltage for the small test voltage applied on secondary
Is This Answer Correct ? | 14 Yes | 151 No |
What is the method to solve circuit using source transformation?
how to compute kvar in substation feeder to improve power factor and sending voltage
what is the impedance voltage of transformer?
1 Answers AVI Enterprises, MacLellan,
There is one 40MVA oil cooled transformer (yet to commission), filled with 95% oil and we are trying to fill 5% Nytrogen in that transformer so that there should not be any foreign component inside. But even though there is no leakage, nytrogen is not withstanding inside transformer, within a day or two pressure guage is showing 0. Why is it soooo? Pls reply.
What is a charge.?
1500Ah VRLA battery,if its weight is designed 125kg during maufacturing its weight is reduced to 85kgs,What will be impact on AH capacity,life & economy?
At which time Synchronous generator act as a Synchronous Condenser?
(1)The demand for electricity , the amount of renewable generation available, the amount of fossil fuel generation available and the cost of the fossil fuel generation are shown in table below period(hrs) demand(MW) renewable (MW) fossil- fuel(MW) cost of fossil fuel(MW) 00.00 - 01.00 2000 1800 2000 30 01.00 - 02.00 2300 2500 2000 30 02.00 - 03.00 2500 2700 2100 45 03.00 - 04.00 2900 3100 2100 50 04.00 - 05.00 2700 2600 2500 45 05.00 - 06.00 2400 2000 2700 50 06.00 - 07.00 2200 1800 2000 36 07.00 - 08.00 2100 1600 2000 36 Assuming that the renewable generation incurs zero cost, determine an optimal generation schedule(specifying the amount of renewable generation and fossil fuel generation used in each period, the cost for each period and the overall cost for 8 hours.)
Why in Hv transmission line as we see there are generally 6 or more than 4 conductor wires are used instead of 4 i.e. 3 for phase and 1 for neutral wire?????
What is the Different b\w Circuit Breaker & Isolater
What is the minimum percentage of power that a powerplant can support in ilanding mode ?
My requirement is 1VA,50/5A Current Transformer for Metering .If I select 15VA , 50/5A CT.Is there any possibility of Technical Problem ?