1)how can calibrate temperature transmitter?
2)how can calibrate flow transmitter?
3)how can calibrate level transmitter?
Answers were Sorted based on User's Feedback
Answer / tontoy
1 prepare the instruments needed in calibrating temp.
transmetter.
2 unsrew the resistance input of the transmetter, and
connect it to a resistance box.
3. unsrew the output side of the transmetter, connect the
ammeter serries with the supply of 24 volts dc.
4. supply it with the resistance of 0% or 100 Ohm until
100%. and record it to the data in the as found.
5. the next is the zeroing. supply the input with 100ohm
resistance. adjust the adjustment of the zero side by
twisting slowly to the left to have an output of 4mA.
6. span- supply the transmitter with 100% depends on the
value of high temperature of the RTD value. and adjust it
to 20mA.
7 repeat it up to 4-5 times.
then supply is again with 100Ohn, mast have an output of
4mA until 100%.
record it to the data as asleft.
for 0% must have an output of 4mA, 25% 8mA, 50% 12mA, 75%
16Ma, and 20mA for 100%.
Is This Answer Correct ? | 101 Yes | 17 No |
Answer / sumit yadav
1)There is equipment available where we can put RTD and
give temperature.Now set temp transmitter parameters to
produce mA equivalent to temp given.
Is This Answer Correct ? | 71 Yes | 26 No |
Answer / gcs
1. First select the calibrating equipment
2. for ex: For RTD, select RTD circuit with zero and span adjustment potentiometers.
3. make the input quantity (temperature) to zero.
4. adjust the zero adjustment pot ntill the output of the RTD becomes zero.
5. make the input quantity to high (Ex.100 deg) and adjust the span pot till the output becomes 100.
6. Repeat steps 3 through 5 till there are no changes in zero and span pot.
7. now the instrument is calibrated.
Is This Answer Correct ? | 13 Yes | 22 No |
Meaning of the following a. IOP- Manimum; b. IOP- Maximu,;
I have a Control VAlve having size of 2 ".Only the known parameter is Pressure drop . Its 2 Kg. Then How to calculate control valve sizing means Cv.
If relative y axis vibration sensor is by passed, and relative x axis and absolute sensor is left working. how much monitoring i would have risked?
Why some transmitter shows flow in MMWC and some in TPH?
is any standard angle for thermowell mounting for horizontal and vertical pipe lines?
what is cascade system ?
why 4-20 mA signal is preferred over a 0-10V signal
how commission a transmitter evev plant is already running
What's the Installtion procedure of DP Transmitter for Gas,steam and water?
Thermocouple is a transducer but rtd is not transducer why? Both taking heat as a input and giving mv
what is puling in n pulling out in flame scanner system?
Can we use a 10000 Lph Flow Transmitter in 100 LPH flow line to get 20mA O/P by adjusting SPAN ?