if 50hz transformer is required to be run on 50% frequency
what needs to be done???????????
Answers were Sorted based on User's Feedback
Answer / pankaj rajput
It will trip on over fluxing protection, if the protection
is installed.
It's not a wise situation to connect transformer to a lower
frequency with same voltage. The flux induced in core is
directly proportional to voltage & inversly proportional to
frequency. Hence the core will be over heated/over fluxed
and may get damage due to over heat.
The only remedy is reducing the voltage in same ratio.
| Is This Answer Correct ? | 31 Yes | 2 No |
Answer / ashokreddyreguri
flux is proportional to E\f or V\f
if the frequency is reduced the ratio V\f will increase so
flux will increase.so to maintain this flux magnetizing
current required will increase.this reduces the no load
power factor , so on load power factor is also reduced.
this also reduces o\p of transformer.so V/f ratio of t/f
must be maintained constant.
as 50% of frequency is applied to maintain constant V/f
input voltage applied must be 50%if rated voltage
| Is This Answer Correct ? | 16 Yes | 0 No |
Answer / eeaadil
60 Hz is expensive to generate and safer to operate than 50 Hz
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / abhishek goyal
Xmer is the static device which can produce the voltage in
secondary side WITHOUT CHANGING OF FREQUENCY. (Pl read xmer
principle. NO CHANGE REQUIRED.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / sachin_pawaskar2001
Nothing............only you will get 25hz frequency at out
put.
| Is This Answer Correct ? | 0 Yes | 24 No |
what is meant by Hrc fuses.?In the distribution system different rating hrc fuses are used for tranformer(which is 3k,6k,10k,15k etc).what is k?.plz any brother tell me about k?
what's the reson that,Load is not same on VFD I/P and O/P Side.whenever DOL condition load is same I/P and O/P side.
I have 4 busbar of 1000 ampere. we use 4 busbar to make 4000 ampere in one phase.my problem is that when we applied 60% load on that then busbar produced high noise.what is the reason of that and how can i minimize that noise.
0 Answers College School Exams Tests,
in our sub station why we step down firstly 33kv\11kv then 11kv to 430v. can we direct step down 33v to 430.v.
how to calculate the output power of vfd , please help me.
what are the deffects for failure of PLC?
two way ckt diagram can be drawn by how many ways? give diagram
Which type of gas used in cylinder (VCB)?????
how to calculate the change over time for star delta starter for different KW motor?
Can the efficiency of transformer be measured with the help of wattmeter readings taken at primary and secondary side? Support the answer.
How much ampere rating on LT side of distribution transformer and also on HT side of 200KVA transformer
what is slip ring startor
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)