Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


in 50 mw generator if field is open in full load running
condition what happen and for protection which relay used?

Answers were Sorted based on User's Feedback



in 50 mw generator if field is open in full load running condition what happen and for protection..

Answer / abid ali khattak

Usually we are using a loss of excitation rely. Which
always getting a sense from the field excitation circuit
continueslly during the runing condition of Generator.

Is This Answer Correct ?    9 Yes 0 No

in 50 mw generator if field is open in full load running condition what happen and for protection..

Answer / a1

I is depend on type of operation-

1) If parrallel with grid/Other generator, than it will
draw reactive power from the Grid/Generator and give active
power to the load. It will work as a Induction Generator.
Reactive power of connected circuit will unbalance.

2) If Generator is running island mode(without any other
source), than terminal voltage of genertor will start to
decrease and current will start to increase. Winding temp.
of Generator and drives will increase.

Under excitation relay provide for this.

Is This Answer Correct ?    4 Yes 1 No

in 50 mw generator if field is open in full load running condition what happen and for protection..

Answer / deepak

it run as induction gen & draw excitation power from grid

Is This Answer Correct ?    5 Yes 3 No

in 50 mw generator if field is open in full load running condition what happen and for protection..

Answer / k.prakashchandra

Loss of excitation relay (LOE)

Is This Answer Correct ?    0 Yes 0 No

in 50 mw generator if field is open in full load running condition what happen and for protection..

Answer / prodip das

It acts as a load, Sensing relay of excitation voltage

Is This Answer Correct ?    0 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

i am going to attaned the engineer (disign)iterview at HAL please give me duid line

0 Answers   HAL,


Following test should be conducted to find out relative polarity of transformenr terminals A no load test B back to back test C phasing out test D none of above

0 Answers  


In pakistan appliances work on 220v at 50hz and in us appliances work on 110v at 60hz what is basic theory to explain it

1 Answers   SNGPL,


how to identified power tranfer line is how much KV????

5 Answers   Essar,


I am new guy as an electrical engr. in a 100MW HFO based power project. I am in operations division. I have noticed from last few days, my supervisor sends the last 24 hours energy generation calculation to my plant manager. I have noticed, he calculated last 24 hour's generated energy differences in KWH then he multiplied it with a multiplying factor 960. for example: total difference =2.685 KWH*960= 2577.6 MWH. but he does not not know what is multiplying factor 960?? can anybody explain it??

1 Answers   Orion,


why the projects getting loss?

0 Answers   SBPL,


Why Nutral CT rating for Earth Fault Protection of Transformer neutral shall be 20% of Full load Current of Transformer

2 Answers  


For a 50MVA (138/69/13.8 KV) transformer, what would be the maximum demand in order not to exceed 80% of its operating capacity.

2 Answers  


what is allowed value of zero sequence impedancce of 6.6 kv nuetral earthing transformer ?what is the actual value

0 Answers  


in ACB breaker requireding 3200Amps. buscoupler getting OFF mode and again it reset and getting normal position give me a required answer?

0 Answers  


Why is the generator rating always in kVA and motor rating in kW?

7 Answers  


Utility company give the supply to customer in KVA but bill them for Watt.why?

1 Answers   L&T,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)