what is effect of unbalaced load -- say R 15A, Y 25A, B 10A
Answers were Sorted based on User's Feedback
Answer / debasis
Resulting neutral current. Generally lighting system has
this type of unbalance. If neutral is not provided then
star point will be shift from its ideal place caused
overvoltage in one or two phase(s).
Is This Answer Correct ? | 15 Yes | 2 No |
Answer / vinod kumar t
unbalanced load wil cause to flow of negative sequence
current which will heats up the alternator and hence it
effects insulation failure
Is This Answer Correct ? | 13 Yes | 2 No |
Answer / ravi teja.a
Resulting flow of neutral current. Generally lighting
system has this type of unbalance. If neutral is not
provided then star point will be shift from its ideal place
to new place with the phase angle related to phase(which
has the higher current value in mentioned phases)caused
over voltage in one or two phase(s).-------is the correct
answer.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / ramesh.r.t
If the supply voltage must 440vac 50Hz in star or delta
connection of motor or alternator stator pitch factor either
phase angel are changed.
Is This Answer Correct ? | 2 Yes | 0 No |
what is mean by PIR in circuitbreaker and give me detail of that?
how can we calculate cable size
What are the various reasons for an inductin motor to get heated?
3phase lt motor winding how to checking with megger
how does damper winding produces torque in synchronous motor?
Why neutral wire is heating in symmetric single phase distribution of three phase power supply?
should %impedance be high or low in a power transformer? if so why?
what are the effects of variations in frequency when you are connected to national grid??
why power factor is lagging and leading(i.e -1to +1)
in conventional fan regulators how the current varies with speed?
two bolbs of 100w and 40w respectively connected in series across a 230v supply.which bolb will glow bright and why?
16 Answers DRDO, PSPCL, Siemens,
Abb 11kv how it is closing automatically when the cb is racking in and rack out when it reaching test position