Initially motor starts with star connection ,after few
timing changes to delta connection, why the motor should
run continously in star connection,it gives high torque &
low current?
Answers were Sorted based on User's Feedback
Answer / madhu
basically in star connection line current is equal to phase
current,it gives high starting torque. after motor reaches
pick up speed we changed to delta.because in delta line
voltage is equal to phase voltage& line current is root 3
times the phase current.if we run in star in running time
the power losses are more due to current is high. thats why
we changed star to delta.
Is This Answer Correct ? | 18 Yes | 3 No |
The purpose of starter is to start the motor and to limit
the starting current.we are starting the motor in y-
connetion during this impedence of two windings put across
the line voltage hence the starting current gettinh
redeuced
but the motor rated capacity (out put torque)can only be
obtained when itis changed to delta connection this time
the voltage is incresed bu 1.732 time to meet the torque
(torque is direct proportion to square of supply voltage .
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / velusamy
There are two reasons
1.To get high starting torque, motor runs at star for
predetermined duration and then changed to delta.
2.If the motor runs continuously , the capacity of the
motor is reduced by root 3 times (Capacity of motor
rating/1.7324) and hence motor will fail if the OL setting
is not reduced to 1.7324times of motor full load current).
Is This Answer Correct ? | 6 Yes | 2 No |
What are options used for earthing the switchgear.
How does "OUT OF STEP" relay ,for Synchronous motor protection, work?
why we r used APFC Panel in industrial area.when P.F. low then wat will be the effect in our system?
10 Answers ABB, Georgio Rocks, Piramal Healthcare, Zenith Engineering Corporation,
a solenoid of inductance 250mH and resistance 10ohm is connected to a battery. the time taken for the magnetic energy to reach 1/4th of its maximum value will be?
explain why reduced voltage starters are required for large tree phase inudction motor
I have a 3 phase 600 volt prim. feed and a 120/208 sec. Isolateing tranformer .We are using this system for safety against shock . What is the proper grounding ?? Does the common on sec. get earth ground ???
in our all power plant have connected in grid and grid voltage and plant voltage is same, but as per as electrical concept the power will transmit from high potential to low potential but here altough same,then how power transmit from power plant to grid.
how we can set the IDMT relay.
Application Comparison between 22KV (UE)and 33KV (E) system. Are we allowed to use 33KV (E) cable in lieu of 22KV (UE) cable. What are the technical disadvantages.
what is the function of 1 phase preventer?
Why neutral has to switch on-off with phase in TN IT TT systems i.e neutral should be taken as fourth pole
what is the full form of ka (100A mccb KA)