In step down transformer (415/200V),mistakenly secondary
side is connected to 415V for some hours, what would be
result of this condition?
Answers were Sorted based on User's Feedback
Answer / ankaraju
The secondary side is rating of 200v,if you considering
loop the net current flowing throw winding increases hence
losses also increases and winding over heated,if it so on
for hours winding insulation may failed.And another one is
core is nearer to low winding,due to high voltage core
losses and core insulation between laminations also failed.
Is This Answer Correct ? | 34 Yes | 5 No |
Answer / milan
secondary side winding turns is designed for 200 volts. If
we give 415v the secondary side winding turns will not
sustain the voltage . For which insulation and winding both
will damage .If we give 415v to secondary the primary will
get 816.125v
Is This Answer Correct ? | 19 Yes | 3 No |
The current at 200v side will be more than what designed
for the transformer and core loss will be more. So
ultimately,transformer will be heated up more faster than
ordinary condition. Depends upon the insulation used for
core construction, and how long u are connected the supply,
there r chances of insulation failiure.
Is This Answer Correct ? | 11 Yes | 1 No |
Answer / manoj
as 2ndary side winding is design for 2oo volt so when we
connect 2ndary side to 415 volt,then after some hour the
2ndary winding burnt.
Is This Answer Correct ? | 9 Yes | 4 No |
Answer / neeraj
the whole transformer will burn up.
i do it practical one time.
but in future i will not do such thing.
Is This Answer Correct ? | 4 Yes | 1 No |
if Secondary puts 415v, than primary wants to take the
voltage upto 850v, & it can burn the winding of the
transformer.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / partha
In this case, the transformer will undergo insulation
degradation. Also due to the increased voltage, the core
losses will increase. The core will be also subjected to
overfluxing which will cause saturation and increased core
losses.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / vino raju dee
200v induced in the primary.there is no application for
this induced voltage.
Is This Answer Correct ? | 0 Yes | 0 No |
What is difinition of HIGH RESISTANCE FAULT and LOW RESISTANCE FAULT?
why we use circuit breakers for switching instead of normal switching device?
How to design the NGR Resistance
How the line trap works in substation...?
why do we use 25kv supply for traction purpose?
What is the difference between DOL starter and star delta starter
I am interested to know what does 15 KVA DG set actually means? If I dont know the DG rating, is it possible to identify KW by simply knowing the diesel consumption?
what is vtg limit of earth and neutral at transformer side?
Why usually in all electrical equipment taking more current in Y pahse like pumps,compressor,or any other applications
Why DC weldings sets preffered over AC considering human safety aspects ?
What is the BS(British Standard)code for 11kv motor
Which capacitor is preferred for high voltage and frequency?