what is pf. how to calculate capacitor bank value to
maintain unity pf.
Answers were Sorted based on User's Feedback
Answer / nilesh kumar singh
Power Factor is defined as the ratio of Real power and
Apparent power.
for calculating Capacitor bank value the formula is :
kVAr = KW {tan(cos^-1 Phi e) - tan(Cos^-1 Phi d)}
Where - Phi e = existing Power Factor.
Phi d = Desired Power Factor.
Is This Answer Correct ? | 101 Yes | 8 No |
Answer / rajendra singh
for calculating Capacitor bank value the formula is :
kVAr = KW {tan(cos^-1 Phi e) - tan(Cos^-1 Phi d)}
Where - Phi e = existing Power Factor.
Phi d = Desired Power Factor.
Is This Answer Correct ? | 42 Yes | 8 No |
Answer / shivappa
to calculate desired capacitor value, the formula is
KVAR= KW(TAN PHI 1 - TAN PHI 2 )
WHERE PHI 1 = EXISTING POWER FACTOR
PHI 2 = REQUIRED POWER FACTOR
Is This Answer Correct ? | 23 Yes | 14 No |
Answer / kim leang
KVAR= KW(TAN PHI 1 - TAN PHI 2 )
WHERE PHI 1 = EXISTING POWER FACTOR
PHI 2 = REQUIRED POWER FACTOR
Is This Answer Correct ? | 14 Yes | 9 No |
Answer / midhun
Calculation and selection of required capacitor rating
Qc = P * {tan [acos (pf1)] - tan [ acos (pf2)]}
Qc = required capacitor output (kVAr)
pf1 = actual power factor
pf2 = target power factor
P = real power (kW)
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / fancy102
hi..i also interested in it..i am carrying out pf
measurement system and i am headache in how to maintain the
unity pf too..
Is This Answer Correct ? | 40 Yes | 36 No |
Answer / ezzuddin
The correct answer and below is the proof of the formula:
KVAR= KW X [√(1–(COSФ)^2)]/COSФ
The proof:
Pythagoras Theorem states that in a right-angled triangle
the square of the hypotenuse is equal to the sum of the
squares of the other two sides.
so that:
Q is the hypotenuse.
S is the opposite.
P is the adjacent.
TanФ= opposite/adjacent = S/P -----> S=P x(TanФ)
Pf=COSФ= adjacent/hypotenuse = P/Q ---->Q=P/COSФ
Pythagoras said that:
Q^2= P^2 + S^2
P^2/(COSФ)^2= P^2 + (P^2 x (TanФ)^2)
by divide P^2:
1/(COSФ)^2 = 1 + (TanФ)^2
by changing the both sides:
(TanФ)^2 = (1/(COSФ)^2) - 1
(TanФ)^2 = (1/(COSФ)^2) - ((COSФ)^2/(COSФ)^2)
by Taking the (1/(COSФ)^2) Common factor:
(TanФ)^2 = {1/(COSФ)^2)} x ( 1 - (COSФ)^2)
by taking the square root:
TanФ = [√(1–(COSФ)^2)]/COSФ
so that:
KVAR = KW x [√(1–(COSФ)^2)]/COSФ
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / santosh
react power kvar=v i sin phi, we know p.f=1,i.e cos phi
calculate sin phi,v i values from total load
Is This Answer Correct ? | 14 Yes | 11 No |
Answer / vekuva
KVAR= KW(TAN PHI 1 - TAN PHI 2 )
WHERE PHI 1 = EXISTING POWER FACTOR ANGLE i.e., COS^¯1(p.f1)
PHI 2 = REQUIRED POWER FACTOR ANGLE i.e., COS^¯1(p.f2)
p.f 1 = EXISTING POWER FACTOR
p.f 2 = REQUIRED POWER FACTOR
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / ezzuddin
The correct answer and below is the proof of the formula:
KVAR= KW X [Sqrt(1–(CosQ)^2)]/CosQ;
The proof:
Pythagoras Theorem states that in a right-angled triangle
the square of the hypotenuse is equal to the sum of the
squares of the other two sides.
so that:
C is the hypotenuse.
S is the opposite.
P is the adjacent.
TanQ= opposite/adjacent = S/P -----> S=P x(TanQ;)
Pf=CosQ;= adjacent/hypotenuse = P/C ---->C=P/CosQ;
Pythagoras said that:
C^2= P^2 + S^2
P^2/(CosQ)^2= P^2 + (P^2 x (TanQ)^2)
by divide P^2:
1/(CosQ)^2 = 1 + (TanQ)^2
by changing the both sides:
(TanQ)^2 = (1/(CosQ)^2) - 1
(TanQ)^2 = (1/(CosQ)^2) - ((CosQ)^2/(CosQ)^2)
by Taking the (1/(COSQ)^2) Common factor:
(TanQ)^2 = {1/(CosQ)^2)} x ( 1 - (CosQ)^2)
by taking the square root:
TanQ; = [Sqrt(1–(CosQ)^2)]/CosQ;
so that:
KVAR = KW x [Sqrt(1–(CosQ)^2)]/CosQ;
Is This Answer Correct ? | 4 Yes | 1 No |
Whta is WT in a transformer, specify its function.
what is short circuit force ? How to calculate it for Panel?
why DG sets power factor is 0.8 lagging.
In explosive and polluted environments which type of motors do we use?
How can a equal potential zone be carried out in conductors?
Why transformer rating in KVA? describe.
For high frequency application we use which transformer?
Hy the hydro power stations have high transmission and Distribution costs?
how does high earth to neutral voltage affect electronic equipment?
What are the protections for safe running of electric generator?
a transformer can have zero voltage regulation a)o pf b)1 pf c)lagg pf d)lead pf
We need to current density & short circuit calculation at 65kA for aluminium & copper busbar.