Answer / m.s.srinivasan
The diesel generating set efficiency is calculated interms
of units generated per liter of diesel consumed.
To monitor either you need to have a diesel flow meter
fitted in the supply as well as the return line after the
governer and the KWHr ( Units )generated.
For less accurate measurement a dip readings can be take
along with the units generated predetermined time.
Is This Answer Correct ? | 63 Yes | 33 No |
Answer / rajendra marathe
Efficiency is the ratio of Outpur/Input. In terms of
Generator, it is considered the efficiency is 80%. 1000KVA
is the Vertual power of Generator. KiloWatt is the actual
power of the generator.On basis of KW the ampere rating
load capacity is calculated. For 1000 KVA , KW is 800. The
ampere rating is =1000x KW/240 for Single phase and for 3
phase =1000xkw/440. The Efficiency can be calculated on the
basis of load ampere it can withstand.
Is This Answer Correct ? | 25 Yes | 14 No |
Answer / jag
The generator efficiency is calculated by units
generated/diesel consumed.
Is This Answer Correct ? | 16 Yes | 8 No |
Answer / faisal
Step 1
Determine the amount of fuel consumed in an hour by the generator. You can use a diesel fuel consumption chart to calculate how much fuel is used in an hour by generators of various sizes.
Step 2
Determine the total electrical power load consumed during an hour. This can be done by connecting a kilowatt-hour meter to the output of the generator, or by referencing the electrical output label on the generator.
Step 3
Convert the amount of fuel used to British Thermal Units, or BTUs. The Oak Ridge National Laboratory has a chart that has the number of BTUs in various types of fossil fuels.
Step 4
Convert the fuel's BTU value to kilowatt-hours by using the conversion factor of 1 kWh = 3413 BTU.
Step 5
Divide the output of the generator in kWh by the input value of the fuel used in kWh. Multiply this figure by 100 to express it as a percent.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / naresh kumar
dear all i want to know the effiency of 250kva dg set
Is This Answer Correct ? | 8 Yes | 5 No |
You did not say what efficiency, whether you get good KWH/ diesel consumption or whether the genset is loaded efficiently
Whatever, you need a KWH METER AND DIESEL CONSUMPTION METER.If you run your 1000KVA gen set for 20 hrs.your genset say at 0.8 pf it could have generated;
1000kva x 0.8 =800KWH per hr .SO FOR 20 Hrs s 16000KWH. If YOUR KWH generated reading says 12000kwh than your generator usage effiociency is 12000/16000 =75%
If the diesel consumption was 600ltrs than kwh/l is
12000/600 =20KWH/Litre diesel. you have to calculate seperately for both of them.
Is This Answer Correct ? | 36 Yes | 34 No |
Answer / sanat khan
Answer
# 4 Units generate/litres consumed
Thanks for Marking this Answer
Answer
# 1 The diesel generating set efficiency is calculated
interms
of units generated per liter of diesel consumed.
To monitor either you need to have a diesel flow meter
fitted in the supply as well as the return line after the
governer and the KWHr ( Units )generated.
For less accurate measurement a dip readings can be take
along with the units generated predetermined time.
Thanks for Marking this Answer 0 M.s.srinivasan
Is This Answer Correct ? | 8 Yes | 9 No |
Answer / manjunatha ac
units generated/ diesel consumed
EX=1000 units generated /350 ltrs consumed
1000/350=3.5 IS dg efficiency.
Is This Answer Correct ? | 3 Yes | 9 No |
Answer / p prudvi krishna
dg set efficiency can be caluclated using forumala that number of units generated divided by total disel consumption ,
disel consumption include on time disel level + pumping during set running-offtime disel level any generator from 320 kva gives an average efficiency of 3.6 to3.8 units per litere
Is This Answer Correct ? | 3 Yes | 10 No |
why star point of motor shall not be grounded?
How would you relate your key competencies to this position?
What is rotating magnetic field?Discuss elaborately.
What is shutdown of electrical sub station?
difference between over current and over load protection?
how i caculate the cable size for power factor correction unit for example 300kvar
design a LV scheme for a 15 storied building?
How many types of earths are there?What is the maximum ohms of earthfit?
what is the use of Antipumping in HT breakers.
There are two nos of 33Kv/11Kv 5MVA transformers conecting through HT cable from substation having metering at substation itself.One transformer used at a time another remains stand by.Further 11 nos of 11Kv/440V transformers are attached on it and each transformer is having its own Power factor correction panel.Now one 33/11Kv transformer at no load condition/Stand by condition is having power factor in leading side upto 0.21 and while when another tranformer at same situation have power factor in lagging 0.42. Now one thing is clear that transformer one is having 1.5 Km long 33kv cable due to that PF goes in leading side and another is having only 250 mtr length remains him lagging. Now i want to know that how i can maintain the Power factor at no load/ stand by position though both are behaving in seperate manner.
if i have 5kw,9A,three phase induction motor,if i want to install it 100 meter away from its feeder,how i will culculate cable size for this load.
I have been using an 600VA with 0.6 p.f UPS with my desktop which has 450W power supply unit. Can anyone explain how can this happen . Because the output of the UPS is 360W (600*0.6) (<450W)